OK, so this is for commercial decks. Is this, or can this be applicable to residential decks?
1604.8.3Decks.
Where supported by attachment to an exterior wall, decks shall be positively anchored to the primary structure and designed for both vertical and lateral loads as applicable. Such attachment shall not be accomplished by the use of toenails or nails subject to withdrawal. Where positive connection to the primary building structure cannot be verified during inspection, decks shall be self-supporting. Connections of decks with cantilevered framing members to exterior walls or other framing members shall be designed for both of the following:- 1.The reactions resulting from the dead load and live load specified in Section 1606 and Table 1607.1, in accordance with Section 1605, acting on all portions of the deck.
- 2.The reactions resulting from the dead load and live load specified in Section 1606 and Table 1607.1, in accordance with Section 1605, acting on the cantilevered portion of the deck, and no live load on the remaining portion of the deck.