1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Ventilation rate

Discussion in 'Mechanical Codes' started by Sifu, Jul 1, 2019.

  1. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    1,178
    Likes Received:
    126
    Looking at IMC t403.3 and/or ASHRAE t6-1, or any other guiding document, does anybody have an idea as to what a "sewing area" be considered when trying to figure out ventilation rates? This is a room where 18 occupants will sit at sewing machines and work.
     
  2. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    701
    Likes Received:
    275
    I'd put it as the same as a computer workroom w/out printing. Most comparable use provided.

    No like sewing machines emit any vapor or create much dust.

    upload_2019-7-1_10-46-30.png
     
  3. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,882
    Likes Received:
    368
    Does the term "sweatshop" mean anything or working under the lights (hot?).
     
  4. rgrace

    rgrace Sawhorse

    Joined:
    Feb 18, 2010
    Messages:
    184
    Likes Received:
    46
    Temperature control and fresh air are two different things. I would agree somewhat with the computer workroom classification, however there is probably quite a difference in the metobolic rates. Perhaps a mix with that and commercial laundry?
     
  5. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,882
    Likes Received:
    368
    As opposed to a dry cleaners?
     
  6. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,701
    Likes Received:
    455
    I'm wondering if commercial laundry ventilation rates assume additional moisture load that needs exhausted that would not be present in this situation.
     
  7. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,882
    Likes Received:
    368
    I am more concerned as to offgassing of dry cleaning chemicals that might impact workers.
     
  8. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,701
    Likes Received:
    455
    Am I missing something? How do you guys sew down there anyway?
     
    rgrace likes this.
  9. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,882
    Likes Received:
    368
    Material floor to ceiling, limited aisles, blocked windows, think Shirtwaist fire years ago.
     
  10. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    198
    Likes Received:
    63
    How is a sewing area any different from any other place where people sit and do assembly work? Does sewing release chemicals? Maybe it is a little dusty...but operators could simply just wear masks to comply with OSHA.
     
  11. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    1,178
    Likes Received:
    126
    I made a site visit and met with the contractor. The use is an open floor where 5 to 7 people will make custom curtains, though I figured my ventilation rate on 18 based on the density. The previous use and existing ventilation exceeded what I think they need based on the what they were doing (using the computer room w/o printing is about the closest thing I could figure) so I am fine with it. Certainly if I thought it would involve dry cleaning, chemicals or a sweat-shop use I would have more concerns but this is none of those things so to them I say have a nice day and I wish them success in their venture.
     
    tmurray likes this.