Do you have a separate energy plans examiner or do you do it yourself? What does your jurisdiction do to ensure compliance with the energy code?
Here are some excerpts from the FBC which mimics the IECC:
Design professionals responsible under Florida law for the design of lighting, electrical, mechanical, and plumbing systems and the building shell, shall certify compliance of those building systems with the code by signing and providing their professional registration number on the energy code form provided as part of the plans and specifications to the building department.
This then goes on to state:
C103.2 Information on construction documents.
Construction documents shall be drawn to scale upon suitable material. Electronic media documents are permitted to be submitted where approved by the code official. Construction documents shall be of sufficient clarity to indicate the location, nature and extent of the work proposed, and show in sufficient detail pertinent data and features of the building, systems and equipment as herein governed. Details shall include, but are not limited to, the following as applicable:
The building’s thermal envelope shall be represented on the construction drawings.
So who amongst you is checking for all of this? Who is not?
Then there are the required inspections such as these:
C104.2.2 Framing and rough-in inspection.
Inspections at framing and rough-in shall be made before application of interior finish and shall verify compliance with the code as to types of insulation and corresponding R-values and their correct location and proper installation; fenestration properties (U-factor, SHGC and VT) and proper installation; and air leakage controls as required by the code and approved plans and specifications.
C104.2.3 Plumbing rough-in inspection.
Inspections at plumbing rough-in shall verify compliance as required by the code and approved plans and specifications as to types of insulation and corresponding R-values and protection; required controls; and required heat traps.
C104.2.4 Mechanical rough-in inspection.
Inspections at mechanical rough-in shall verify compliance as required by the code and approved plans and specifications as to installed HVAC equipment type and size; required controls, system insulation and corresponding R-value; system and damper air leakage; and required energy recovery and economizers.
C104.2.5 Electrical rough-in inspection.
Inspections at electrical rough-in shall verify compliance as required by the code and approved plans and specifications as to installed lighting systems, components and controls; and installation of an electric meter for each dwelling unit.
C104.2.6 Final inspection.
The building shall have a final inspection and shall not be occupied until approved. The final inspection shall include verification of the installation and proper operation of all required building controls, and documentation verifying activities associated with required building commissioning have been conducted and findings of noncompliance corrected. Buildings, or portions thereof, shall not be considered for a final inspection until the code official has received a letter of transmittal from the building owner acknowledging that the building owner has received the Preliminary Commissioning Report as required in Section C408.2.4.
Here are some excerpts from the FBC which mimics the IECC:
Design professionals responsible under Florida law for the design of lighting, electrical, mechanical, and plumbing systems and the building shell, shall certify compliance of those building systems with the code by signing and providing their professional registration number on the energy code form provided as part of the plans and specifications to the building department.
This then goes on to state:
C103.2 Information on construction documents.
Construction documents shall be drawn to scale upon suitable material. Electronic media documents are permitted to be submitted where approved by the code official. Construction documents shall be of sufficient clarity to indicate the location, nature and extent of the work proposed, and show in sufficient detail pertinent data and features of the building, systems and equipment as herein governed. Details shall include, but are not limited to, the following as applicable:
- Insulation materials and their R-values.
- Fenestration U-factors and solar heat gain coefficients (SHGCs).
- Area-weighted U-factor and solar heat gain coefficient (SHGC) calculations.
- Mechanical system design criteria.
- Mechanical and service water heating system and equipment types, sizes and efficiencies.
- Economizer description.
- Equipment and system controls.
- Fan motor horsepower (hp) and controls.
- Duct sealing, duct and pipe insulation and location.
- Lighting fixture schedule with wattage and control narrative.
- Location of daylight zones on floor plans.
- Air sealing details.
The building’s thermal envelope shall be represented on the construction drawings.
So who amongst you is checking for all of this? Who is not?
Then there are the required inspections such as these:
C104.2.2 Framing and rough-in inspection.
Inspections at framing and rough-in shall be made before application of interior finish and shall verify compliance with the code as to types of insulation and corresponding R-values and their correct location and proper installation; fenestration properties (U-factor, SHGC and VT) and proper installation; and air leakage controls as required by the code and approved plans and specifications.
C104.2.3 Plumbing rough-in inspection.
Inspections at plumbing rough-in shall verify compliance as required by the code and approved plans and specifications as to types of insulation and corresponding R-values and protection; required controls; and required heat traps.
C104.2.4 Mechanical rough-in inspection.
Inspections at mechanical rough-in shall verify compliance as required by the code and approved plans and specifications as to installed HVAC equipment type and size; required controls, system insulation and corresponding R-value; system and damper air leakage; and required energy recovery and economizers.
C104.2.5 Electrical rough-in inspection.
Inspections at electrical rough-in shall verify compliance as required by the code and approved plans and specifications as to installed lighting systems, components and controls; and installation of an electric meter for each dwelling unit.
C104.2.6 Final inspection.
The building shall have a final inspection and shall not be occupied until approved. The final inspection shall include verification of the installation and proper operation of all required building controls, and documentation verifying activities associated with required building commissioning have been conducted and findings of noncompliance corrected. Buildings, or portions thereof, shall not be considered for a final inspection until the code official has received a letter of transmittal from the building owner acknowledging that the building owner has received the Preliminary Commissioning Report as required in Section C408.2.4.