1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Water heater temperature requirement from inspector

Discussion in 'Plumbing Codes' started by Hyrax4978, Dec 29, 2017.

  1. Hyrax4978

    Hyrax4978 Registered User

    Joined:
    Nov 28, 2016
    Messages:
    45
    Likes Received:
    0
    We recently were asked by the building inspector to change the pre-set temps on the water heaters from 120 down to 110. he said its an ADA code. I was not there for the inspection so i could not question him. but this is news to me. has anyone seen this, or run into this before?

    Thanks,
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
  3. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,808
    Likes Received:
    568
    It does not matter what ADA says the temperature limit is you do not control it by limiting the water heater
    ICC/ANSI
    607.8 Water Temperature.
    Bathtubs shall deliver water that is 120°F (49°C) maximum.
    608.8 Water Temperature.
    Showers shall deliver water that is 120°F (49°C) maximum.

    ADA
    607.6 Shower Spray Unit and Water. A shower spray unit with a hose 59 inches (1500 mm) long minimum that can be used both as a fixed-position shower head and as a hand-held shower shall be provided. The shower spray unit shall have an on/off control with a non-positive shut-off. If an adjustable-height shower head on a vertical bar is used, the bar shall be installed so as not to obstruct the use of grab bars. Bathtub shower spray units shall deliver water that is 120°F (49°C) maximum.

    IPC
    HOT WATER. Water at a temperature greater than or equal to 110°F (43°C).
    TEMPERED WATER. Water having a temperature range between 85°F (29°C) and 110°F (43°C).

    408.3 Bidet water temperature.
    The discharge water temperature from a bidet fitting shall be limited to a maximum temperature of 110°F (43°C) by a water temperature limiting device conforming to ASSE 1070 or CSA B125.3.

    416.5 Tempered water for public hand-washing facilities.
    Tempered water shall be delivered from lavatories and group wash fixtures located in public toilet facilities provided for customers, patrons and visitors. Tempered water shall be delivered through an approved water-temperature limiting device that conforms to ASSE 1070 or CSA B125.3.

    424.3 Individual shower valves.
    Individual shower and tub-shower combination valves shall be balanced-pressure, thermostatic or combination balanced-pressure/thermostatic valves that conform to the requirements of ASSE 1016 or ASME A112.18.1/CSA B125.1 and shall be installed at the point of use. Shower and tub-shower combination valves required by this section shall be equipped with a means to limit the maximum setting of the valve to 120°F (49°C), which shall be field adjusted in accordance with the manufacturer’s instructions. In-line thermostatic valves shall not be utilized for compliance with this section.

    424.4 Multiple (gang) showers.
    Multiple (gang) showers supplied with a single-tempered water supply pipe shall have the water supply for such showers controlled by an approved automatic temperature control mixing valve that conforms to ASSE 1069 or CSA B125.3, or each shower head shall be individually controlled by a balanced-pressure, thermostatic or combination balanced-pressure/thermostatic valve that conforms to ASSE1016 or ASME A112.18.1/CSA B125.1 and is installed at the point of use. Such valves shall be equipped with a means to limit the maximum setting of the valve to 120°F (49°C), which shall be field adjusted in accordance with the manufacturers’ instructions.

    424.5 Bathtub and whirlpool bathtub valves.
    The hot water supplied to bathtubs and whirlpool bathtubs shall be limited to a maximum temperature of 120°F (49°C) by a water-temperature limiting device that conforms to ASSE 1070 or CSA B125.3, except where such protection is otherwise provided by a combination tub/shower valve in accordance with Section 424.3.

    501.2 Water heater as space heater.
    Where a combination potable water heating and space heating system requires water for space heating at temperatures higher than 140°F (60°C), a master thermostatic mixing valve complying with ASSE 1017 shall be provided to limit the water supplied to the potable hot water distribution system to a temperature of 140°F (60°C) or less. The potability of the water shall be maintained throughout the system.

    501.6 Water temperature control in piping from tankless heaters.
    The temperature of water from tankless water heaters shall be not greater than 140°F (60°C) where intended for domestic uses. This provision shall not supersede the requirement for protective shower valves in accordance with Section 424.3.
     
  4. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,486
    Likes Received:
    117
    ADA is not a code but if the International Plumbing Code is used in your area the maximum temperature for sinks is 110.
     
  5. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,471
    Likes Received:
    407
    He might be confused with the requirement for tempered water at hand washing facilities;


    416.5 Tempered water for public hand-washing facilities.


    Tempered water shall be delivered from lavatories and group


    wash fixtures located in public toilet facilities provided for

    customers, patrons and visitors. Tempered water shall be

    delivered through an approved water-temperature limiting


    device that conforms to ASSE 1070 or CSA B125.3.



    TEMPERED WATER. Water having a temperature range


    between 85°F (29°C) and 110°F (43°C).
     
  6. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    415
    deleted repeat of mtlogcabin answer!

    2012 IECC

    C404.3 Temperature controls. Service water-heating equipment shall be provided with controls to allow a setpoint of 110°F (43°C) for equipment serving dwelling units and 90°F (32°C) for equipment serving other occupancies. The outlet temperature of lavatories in public facility rest rooms shall be limited to 110°F (43°C).
     
    #6 Francis Vineyard, Dec 29, 2017
    Last edited: Dec 29, 2017
  7. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    1,020
    Likes Received:
    65
    Assuming IPC is the adopted code.........Aside from all of the other specific posts, IPC 607.1.1 (2012) specifically prohibits the water heater from being the controlling mechanism for either hot or tempered water. Sounds like he may be misremembering a mixture of codes.
     
  8. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,564
    Likes Received:
    217
    He is correct as to 110 degrees
    He is incorrect as to his quoted source.
    Now you know, "the rest of the story"
     
    jar546 likes this.
  9. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,656
    Likes Received:
    244
    It completely depends on what the water heater serves. What exactly is this for and what fixtures are served by the water heater?
     
  10. Msradell

    Msradell Sawhorse

    Joined:
    Jul 23, 2011
    Messages:
    766
    Likes Received:
    60
    I thought that 120° was the accepted minimum because anything lower than that allows bacterial growth in the tank.
     
  11. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    9,743
    Likes Received:
    574
    Though not the case in this instance, Almost Everyone uses the term "ADA" for Accessibility codes. Though not the correct term, almost everyone immediately understands.
     