1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

What Wire Size Is Required?

Discussion in 'Electrical Codes' started by jar546, Nov 22, 2018.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,032
    Likes Received:
    518
    If you were to inspect this AC unit in an industrial warehouse that is fed by a 120/240 Delta with a 208 High Leg, and this was a single phase 240 fed by a double pole breaker, what wire size would you expect to see for this interior installation if the circuit was piped in with EMT to FMC?

    Would you check the position of the breaker in the panel or is it not relevant?

    IMG_1822.JPG
     
  2. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    Is this unit on a roof top or ground set up? Is there a temp adjustment needed? What size conduit?
     
  3. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,032
    Likes Received:
    518
    RJJ

     
  4. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    I would check! AT Least an 8
     
  5. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,774
    Likes Received:
    253
    @ ~ @

    RJJ,

    Why check the position the breaker, and what Article \
    Table would specify the AWG # 8 ?.....Also, what
    edition of the NEC is applicable ?

    Thanks !


    @ ~ @
     
  6. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,032
    Likes Received:
    518
    #8 THHN is only good for 50A. This is not a 208 Wye
     
  7. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    8,335
    Likes Received:
    884
    Prudence calls for qualifying the statement. #8 THHN is only good for 50A if all terminals etc. are rated at 75°.... it is not a # used for deration purposes.

    The equipment in your exercise was manufactured in 2002 and Shirley, the rest of the installation is an open question.
     
  8. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,032
    Likes Received:
    518
    The Minimum Circuit Ampacity for this HVAC unit is 55A, therefore a #6 wire is required. Since there were only 2 current carrying conductors in the conduit and this is an interior installation, no derating was required.
     
  9. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    Without seeing the breaker off the top of my head was the # 8. There are many factors to be considered. How far away is the breaker and under which code. Wire size to my knowledge has not changed over the last three code cycles.
     