Where is Business (B) occupancy under Section 903?

Group B buildings generally don't require sprinkler systems. HOWEVER, corridor protection requirements in other sections, including smoke & fire dampers, can cost as much as sprinklers, and hinder future flexibility to rearrange the spaces.
 
B occupancies (other than the one you mention) do not require sprinkler systems based on fire area, occupant load, or any other criteria, except when an increase in height or area is desired, or when any of the conditions listed in Section 903.2.11 apply.
 