Can anyone think of a way it is permissible to have a 2nd story bedroom in an R-2 occupancy (frat house) without an exterior emergency means of egress? The house has a sprinkler system. I've looked at IFC 2012 1029.1. TIA.
How does a person in the room reach the skylight, open it and get out ?Chad Pasquini said:I have approved a skylight that met the minimum opening requirements.
NOT Permitableoxfordethan said:Can anyone think of a way it is permissible to have a 2nd story bedroom in an R-2 occupancy (frat house) without an exterior emergency means of egress? The house has a sprinkler system. I've looked at IFC 2012 1029.1. TIA.
I believe this is the 2009 IFC... Our state has adopted 2012. It doesn't give the "sprinkler exception".cda said:Build it under the 2009 IBC1029.1 General. In addition to the means of egress required by this chapter, provisions shall be made for emergency escape and rescue in Group R and I-1 occupancies. Basements and sleeping rooms below the fourth story above grade plane shall have at least one exterior emergency escape and rescue opening in accordance with this section. Where basements contain one or more sleeping rooms, emergency escape and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Such openings shall open directly into a public way or to a yard or court that opens to a public way.
Exceptions:
1. In other than Group R-3 occupancies, buildings equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
Frat wanted to add some bedrooms on the second floor of the house. They were advised to submit plans to SFM for approval even though they were informed that a windowless bedroom would not fly. They submitted plans but never received an approval letter or stamped prints. They decided to build it out over the summer while the house was unoccupied. I got a call from the house wanting the number for a sprinkler company to move sprinkler heads. I asked for what reason. That's how I found out.cda said:Why are there no windows?
What year edition are you looking atcballinger said:Came across this when searching for another issue. Sorry I'm late to the discussion, but thought I'd add some input as we've come across this issue a lot here recently. Section 1029.1 only applies to Group R-2s that are using Tables 1021.2(1) or 1021.2(2) for stories with a single exit. If they have access to 2 exits from the 2nd floor, they wouldn't require emergency escape and rescue openings in the bedrooms. (i.e. two exits available on 1st floor, with 2 exit access stairs on 2nd floor). Do they have 2 stairways from 2nd floor?
2012 IBC and I believe he is correctcda said:What year edition are you looking at
It's on my Christmas list.cda said:anyone have 2012 commentary?
101 for those that want to see itRFDACM02 said:As an NFPA "only" inspector, what is the IBC escape window size requirement? I'm wondering how far off the Life Safety Code and the IBC are in this area?