• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

WW A FM do?

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
fire truck goes to building with dry pipe sprinkler system

systems has tripped no fire, no heads open

Friday midnight

sprinkler company cannot make it till monday

Fire alarm will not shut up, because there is still pressure on the switch, monitoring only for the panel, no other significant devices

Options???

drain the system an shut off, so you can silence the fire alarm???

leave system tripped, and shut the fire alarm panel down completly??? that way at least you have sprinkler protection

Other??????
 
who is the responsible party, have them drain the system, reset fire alarms, have them set up a fire watch, get a new sprinkler company
 
This FM would keep the system charged, order local fire watch (for alarm notification) with documentation/verification means and tell the crew to head back to the station. This would only be done after I verified that the owner's sprinkler service firm didn't have emergency service available. On Monday I would request/verify their fire watch documentation and time for system repair and findings.
 
I agree with FM Burns leave it in service as long no problem with freezing temperatures.

Sometimes below the water flow switch is a 1/2" quarter turn shut off valve. If you turn off the valve the water flow will stop and the alarm too. If you are really lucky below the switch will be a valve connect to a small 1/4" copper line to a drain that can be opened to drain the water pressure. IF who ever installed the system installed the required signage, look for the "alarm" sign and follow it to the flow switch. IF not look for the water line below the dry pipe valve and follow it it will take you to the water flow switch.
 
I thought you could not have a shutoff to the flow/high pressure switch?

At least a non monitored one
 
Cda

See IBC 2009 Ed, section 903.4 exception number 7, they only need to be locked and or sealed. This the NJ edition, do not know if this is true outside of NJ.
 
Hummmmm, tried to get that once and was told it is in violation of 13,

Will have to check 13

Thanks for the reference
 
Oh it is required by NFPA 13 and or 72. BUT not the IBC for what ever reason. I find them closed, on pre-action and deluge on dry pipe valves all the time.
 
Insurance Engineer said:
Oh it is required by NFPA 13 and or 72. BUT not the IBC for what ever reason. I find them closed, on pre-action and deluge on dry pipe valves all the time.
Does anyone know if a shutoff to a dry pipe high pressure/ flow switch is allowed per 13???
 
In accordance with NFPA 13, 2010 edition, there can be and probably will be an Alarm Test Shutoff valve. if you possess the NFPA commentary, page 385 Exhibit 8.49, section 8.17.1.4.2, the options call for electronic supervision, locks or seals acceptable to the AHJ.
 