The new code section "SECTION R315 SLEEPING LOFTS" in the International Residential Code outlines the requirements for sleeping lofts in dwelling units and sleeping units. This summary provides a concise overview of the key points covered in this section.
- Definition and Scope:
- Sleeping lofts provided in dwelling units or sleeping units must comply with the code as modified by Sections R315.2 through R315.5.
- Sleeping lofts constructed per this section are considered part of the story below and do not contribute to the number of stories.
- Exceptions:
- Sleeping lofts are exempt from Section R315 if they meet any of the following conditions:
- Depth is less than 3 feet (914 mm).
- Floor area is less than 35 square feet (3.3 m²).
- No permanent means of egress is provided.
- Sleeping lofts are exempt from Section R315 if they meet any of the following conditions:
- Limitations:
- Floor area must be less than 70 square feet (6.5 m²).
- Ceiling height cannot exceed 7 feet (2134 mm) for more than half of the floor area.
- Ceiling Height and Floor Area:
- Clear height below the sleeping loft floor must be at least 7 feet (2134 mm).
- Ceiling height above the finished floor of the sleeping loft must be at least 3 feet (914 mm).
- Spaces with sloped ceilings under 3 feet (914 mm) do not contribute to the sleeping loft floor area.
- Egress Requirements:
- A permanent means of egress must be provided for sleeping lofts, complying with Section R318 and Sections R315.5.1 through R315.5.3.
- Ceiling height for the entire width of the egress path must be at least 3 feet (914 mm).
- Stairways providing egress must meet specific width, tread, riser, and landing requirements.
- Ladders used as egress must have specific rung width, spacing, load capacity, and incline requirements.