• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Understanding NEC 694.7(D) Overvoltage Protection of Wind Electric Systems

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,095
Location
Somewhere Too Hot & Humid
The code reads:

(D) Overvoltage Protection.
A listed surge protective device shall be installed between a wind electric system and any loads served by the premises electrical system. The SPD shall be permitted to be a Type 3 SPD on the circuit serving a wind electric system or a Type 2 SPD located anywhere on the load side of the service disconnect. SPDs shall be installed in accordance with Part II of Article 242.

What it means is:
Wind electric systems often feature towers that are among the tallest structures in a given area. To safeguard these systems and the associated premises wiring against lightning, the implementation of surge-protective devices is essential. These devices are discussed in Article 242, which focuses on Overvoltage Protection.

Furthermore, specific grounding requirements for towers and guy wires are detailed in sections 694.40(B)(3) and (B)(4) of the NEC. To ensure comprehensive protection of wind turbines from lightning strikes, it is also advised to refer to Chapter 9 of the NFPA 780, which is the Standard for the Installation of Lightning Protection Systems. These guidelines provide a framework for effectively securing wind electric systems from lightning-related damage.
 