The 2015 IRC has the following special requirements for sunrooms. Here is a link to get the sunroom book that you are required to design by:
R301.2.1.1.1 Sunrooms. Sunrooms shall comply
with AAMA/NPEA/NSA 2100. For the purpose of
applying the criteria of AAMA/NPEA/NSA 2100
based on the intended use, sunrooms shall be identified
as one of the following categories by the permit
applicant, design professional or the property owner
or owner’s agent in the construction documents.
Component and cladding pressures shall be used for
the design of elements that do not qualify as main
windforce-resisting systems. Main windforce-resisting
system pressures shall be used for the design of
elements assigned to provide support and stability
for the overall sunroom.
Category I: A thermally isolated sunroom with
walls that are open or enclosed with insect
screening or 0.5 mm (20 mil) maximum thickness
plastic film. The space is nonhabitable and
unconditioned.
Category II: A thermally isolated sunroom with
enclosed walls. The openings are enclosed with
translucent or transparent plastic or glass. The
space is nonhabitable and unconditioned.
Category III: A thermally isolated sunroom with
enclosed walls. The openings are enclosed with
translucent or transparent plastic or glass. The
sunroom fenestration complies with additional
requirements for air infiltration resistance and
water penetration resistance. The space is nonhabitable
and unconditioned.
Category IV: A thermally isolated sunroom with
enclosed walls. The sunroom is designed to be
heated or cooled by a separate temperature control
or system and is thermally isolated from the
primary structure. The sunroom fenestration
complies with additional requirements for water
penetration resistance, air infiltration resistance
and thermal performance. The space is nonhabitable
and conditioned.
Category V: A sunroom with enclosed walls.
The sunroom is designed to be heated or cooled
and is open to the main structure. The sunroom
fenestration complies with additional requirements
for water penetration resistance, air infiltration
resistance and thermal performance. The
space is habitable and conditioned.
R301.2.1.2 Protection of openings. Exterior glazing in
buildings located in windborne debris regions shall be
protected from windborne debris. Glazed opening protection
for windborne debris shall meet the requirements
of the Large Missile Test of ASTM E 1996 and ASTM
E 1886 as modified in Section 301.2.1.2.1. Garage door
glazed opening protection for windborne debris shall
meet the requirements of an approved impact-resisting
standard or ANSI/DASMA 115.
Exception: Wood structural panels with a thickness
of not less than 7/16 inch (11 mm) and a span of not
more than 8 feet (2438 mm) shall be permitted for
opening protection. Panels shall be precut and
attached to the framing surrounding the opening
containing the product with the glazed opening. Panels
shall be predrilled as required for the anchorage
method and shall be secured with the attachment
hardware provided. Attachments shall be designed
to resist the component and cladding loads determined
in accordance with either Table R301.2(2) or
ASCE 7, with the permanent corrosion-resistant
attachment hardware provided and anchors permanently
installed on the building. Attachment in
accordance with Table R301.2.1.2 is permitted for
buildings with a mean roof height of 45 feet (13, 728
mm) or less where the ultimate design wind speed,
Vult, is 180 mph (290 kph) or less.