Bypass door hardware @ Adaptable units

Chnelson

REGISTERED
Joined
Jun 17, 2021
Messages
10
Location
Southern California
In order for a unit to be considered adaptable do the bypass closet doors need to have ADA compliant pulls or can they be added later when converting an adaptable unit to accessible?
 
ANSI A117.1-2009 does not have any requirements for storage facilities within Type B units. So, I would say the doors can also be adaptable by adding hardware only if needed.
 
Hi, and welcome. You question is a bit confusing, because you ask about "ADA compliant pulls" but your subject line refers to "adaptable units".
The word "adaptable" implies that it is subject to CBC 11A for privately funded housing, and not subject to ADA for public housing units.

Assuming it is private housing, maybe your question is: can bypass closet doors be installed in an 11A adaptable dwelling unit without requiring the ability to grasp the opening hardware?

If so, look at 1132A.8 for 11A adaptable hardware. The scope of this is particular to "Latching and locking doors that are hand activated and on an accessible route". Assuming for the moment that you have a conventional shallow bedroom closet (for example, about 28" deep) it is not designed to have an accessible route through the doorway and inside the closet. Therefore since it is not on an accessible route, the scope of 1132A.8 does not apply, and the hardware does not need special accessibility features (such as the kind of "ADA"-type pulls that would be found on accessible public housing).

Loom forward to hearing the opinions of others.
 
Hi, and welcome. You question is a bit confusing, because you ask about "ADA compliant pulls" but your subject line refers to "adaptable units".
The word "adaptable" implies that it is subject to CBC 11A for privately funded housing, and not subject to ADA for public housing units.

Assuming it is private housing, maybe your question is: can bypass closet doors be installed in an 11A adaptable dwelling unit without requiring the ability to grasp the opening hardware?

If so, look at 1132A.8 for 11A adaptable hardware. The scope of this is particular to "Latching and locking doors that are hand activated and on an accessible route". Assuming for the moment that you have a conventional shallow bedroom closet (for example, about 28" deep) it is not designed to have an accessible route through the doorway and inside the closet. Therefore since it is not on an accessible route, the scope of 1132A.8 does not apply, and the hardware does not need special accessibility features (such as the kind of "ADA"-type pulls that would be found on accessible public housing).

Loom forward to hearing the opinions of others.
I apologize for any confusion. The project is a privately funded apartment complex. The bypass closet hardware spec was for recessed finger pulls, the owner of the project wanted to change to a different style of pull for these doors. It created a lot of added work because the doors were already prepped for the original hardware that was in the specifications. The pull they changed to happens to be ADA compliant. All the units in the project are 'Adaptable'. They are rejecting the change order for the pulls they changed to and are claiming that the original pulls, in the specification, were wrong because they were not ADA compliant and that adaptable units must, by code, have ADA pulls on bypass closet doors. We are looking for good data to refute this and everything we're seeing regarding what makes a unit 'adaptable' does not address this issue. Further, it is our understanding that converting a unit from adaptable to accessible is something that needs to be able to be done without major 'reconstruction' and should be able to be completed in a couple of days. Certainly installing ADA compliant wire pulls on bypass doors doesn't take a lot of time.
 
Chnelson, you still didn't say where the project was located. I will continue to assume it is in California.
When CBC 11A requires private covered multifamily dwelling unit to be adaptable, and the unit is permitted and constructed and received a certificate of occupancy in compliance with CBC 11A, you have met all the requirements of CBC 11A. There are no post-construction accessibility requirements for the architect or contractor in CBC 11A.
At this point, the Fair Housing Act (FHA) and takes over, and in California also the Unruh Act. The apartment tenant must make a request to the Owner for a "reasonable accommodation" to further modify their apartment to help them with their disabilities. At the end of their residency, the tenant can even be held responsible (via security deposit, escrow, or other negotiated means) for the cost of restoring the apartment back to its original condition.
 
Hi, and welcome. You question is a bit confusing, because you ask about "ADA compliant pulls" but your subject line refers to "adaptable units".
The word "adaptable" implies that it is subject to CBC 11A for privately funded housing, and not subject to ADA for public housing units.

Assuming it is private housing, maybe your question is: can bypass closet doors be installed in an 11A adaptable dwelling unit without requiring the ability to grasp the opening hardware?

If so, look at 1132A.8 for 11A adaptable hardware. The scope of this is particular to "Latching and locking doors that are hand activated and on an accessible route". Assuming for the moment that you have a conventional shallow bedroom closet (for example, about 28" deep) it is not designed to have an accessible route through the doorway and inside the closet. Therefore since it is not on an accessible route, the scope of 1132A.8 does not apply, and the hardware does not need special accessibility features (such as the kind of "ADA"-type pulls that would be found on accessible public housing).

Loom forward to hearing the opinions of others.
If intended for a disabled tenant it is still best practice for "all" operating hardware to be accessible and the closet would require low height clothes poles too.
 
ADAguy, in post #5, the original poster made it clear this was not about a specific intended future tenant with a disability. It was about an owner wanting different closet pulls and then trying to make the contractor (and/or architect?) pay for it by claiming that it was required by code and somehow missed in the original construction.

Here's the reference from the FHA Design Manual regarding modifications that exceed code requirements:

1624031925291.png
1624031983682.png
1624032006239.png
 
Chnelson, you still didn't say where the project was located. I will continue to assume it is in California.
When CBC 11A requires private covered multifamily dwelling unit to be adaptable, and the unit is permitted and constructed and received a certificate of occupancy in compliance with CBC 11A, you have met all the requirements of CBC 11A. There are no post-construction accessibility requirements for the architect or contractor in CBC 11A.
At this point, the Fair Housing Act (FHA) and takes over, and in California also the Unruh Act. The apartment tenant must make a request to the Owner for a "reasonable accommodation" to further modify their apartment to help them with their disabilities. At the end of their residency, the tenant can even be held responsible (via security deposit, escrow, or other negotiated means) for the cost of restoring the apartment back to its original condition.
Yes, it is in California. Once the COO is granted we are really no longer involved...typically. Our main interest at this point is being able to establish that the bypass pulls in an adaptable unit are not required by code to be ADA compliant. The pulls called for in the hardware specification were not ADA compliant and we provided what was specified. As I mentioned, they changed them after the contract was awarded and it resulted in additional costs. We submitted a changed order to cover those costs and they are now rejecting that change order. Their rejection is based on their claim that the pulls should have been compliant from the beginning, that we should have known that, and the contract requires us to meet the code.
 
ADAguy, in post #5, the original poster made it clear this was not about a specific intended future tenant with a disability. It was about an owner wanting different closet pulls and then trying to make the contractor (and/or architect?) pay for it by claiming that it was required by code and somehow missed in the original construction.

Here's the reference from the FHA Design Manual regarding modifications that exceed code requirements:

View attachment 7998
View attachment 7999
View attachment 8000
Making the Architect pay? That would be a first! They want us to eat the cost, which included repairing all of the doors that had been prepped for the originally specified pull, prepping them for the new pull, along with buying the new pulls after already purchasing the originally specified pulls. Jamming it down our throats, so to speak. We are the 'little, lowly' subcontractor and they are the big, powerful developer/builder. They are flexing their muscle by simply declaring we 'should have' known and superseded what the Architect had called for because of it being a code issue. Incidentally, this is not our first rodeo, we have done thousands of adaptable units where the bypass pulls have not been required to be ADA compliant. There is no precedent for this and that's based on our experience in these matters. Unfortunately, from all we can see, the code doesn't specifically state that 'bypass pulls do not have to be ADA compliant in an adaptable dwelling' so it leaves it to interpretation and, of course, their interpretation is that it is required.
 
Making the Architect pay? That would be a first! They want us to eat the cost, which included repairing all of the doors that had been prepped for the originally specified pull, prepping them for the new pull, along with buying the new pulls after already purchasing the originally specified pulls. Jamming it down our throats, so to speak. We are the 'little, lowly' subcontractor and they are the big, powerful developer/builder. They are flexing their muscle by simply declaring we 'should have' known and superseded what the Architect had called for because of it being a code issue. Incidentally, this is not our first rodeo, we have done thousands of adaptable units where the bypass pulls have not been required to be ADA compliant. There is no precedent for this and that's based on our experience in these matters. Unfortunately, from all we can see, the code doesn't specifically state that 'bypass pulls do not have to be ADA compliant in an adaptable dwelling' so it leaves it to interpretation and, of course, their interpretation is that it is required.
Was an AIA construction agreement and general conditions used for the project?
 
They are flexing their muscle by simply declaring we 'should have' known and superseded what the Architect had called for because of it being a code issue. Incidentally, this is not our first rodeo, we have done thousands of adaptable units where the bypass pulls have not been required to be ADA compliant. There is no precedent for this and that's based on our experience in these matters. Unfortunately, from all we can see, the code doesn't specifically state that 'bypass pulls do not have to be ADA compliant in an adaptable dwelling' so it leaves it to interpretation and, of course, their interpretation is that it is required.
How does it leave things open to interpretation?
Flip the discussion: Ask them to provide a code citation where it explicitly IS required.
And RGLA's comment is especially pertinent: the AIA A201 docs do not require the contractor to possess design/interpretation knowledge.
 
Have them look at Section 3.2.3, if they did not delete it or modify it:

The Contractor is not required to ascertain that the Contract Documents are in accordance with applicable laws, statutes, ordinances, codes, rules and regulations, or lawful orders of public authorities, but the Contractor shall promptly report to the Architect any nonconformity discovered by or made known to the Contractor as a request for information in such form as the Architect may require."​
 
How does it leave things open to interpretation?
Flip the discussion: Ask them to provide a code citation where it explicitly IS required.
And RGLA's comment is especially pertinent: the AIA A201 docs do not require the contractor to possess design/interpretation knowledge.
Good stuff and we will use it! Thanks
 
How does it leave things open to interpretation?
Flip the discussion: Ask them to provide a code citation where it explicitly IS required.
And RGLA's comment is especially pertinent: the AIA A201 docs do not require the contractor to possess design/interpretation knowledge.
Yes, but at a minimum he is expected to know code, no?
He is supposed to inform AOR if he runs into an issue like this before proceeding.
Wasn't AOR suppose to receive and approve submittals?
 
Yes, but at a minimum he is expected to know code, no?
He is supposed to inform AOR if he runs into an issue like this before proceeding.
Wasn't AOR suppose to receive and approve submittals?
Q1: It depends. An electrician and plumber, for example, know what is code as to the installation of their respective systems, but they are not required to review the documents to determine whether the electrical engineer or plumbing engineer properly sized the wires or pipes for the design loads or demands. A glazer typically knows that Cat II safety glass is required within doors, even if the contract documents do not show it.

Q2: The problem here is that the doors are not required to be ADA-compliant, so there is no need to inform the architect of the "issue" since there technically is no "issue"--the developer/owner is making it an issue. There is no way for a contractor or subcontractor to foretell that such an issue will occur.

Q3: This depends on what is required in the contract documents. Some architects hate submittals and reduce them down to the bare minimum. Just because a submittal is required or not, does not relieve the contractor from complying with the contract documents. If the contract documents call for one type of pull and the contractor changed it thinking the specified pull was wrong for the situation, the contractor would be liable for any costs to correct it to comply with the contract documents. If the contractor provided what was on the contract documents and the owner wants to change it, then the cost is on the owner. If the contractor submitted the pull per the contract documents before ordering them and preparing the doors for them (which they should), and the architect reviewed and approved it, it would be difficult for the owner to make a claim that it was the wrong pull.
 
ADAguy, note that the original poster did not say that the inspector wrote up a correction. He did say the units were were privately funded, so therefore they are not ADA units. Knowing the code he would not need to provide ADA compliant pulls in order to meet code.

Now, if the construction documents (CDs) that are part of the construction contract actually said "provide and install ADA-compliant hardware at ALL doors", then he would be under a contractual (but not code) obligation. This assumes of course that a set of plans was explicitly referenced in the contract for construction. He would be wise to ask for clarification as to what constitutes ADA-compliant hardware prior to signing the contract.
*
Let's use another example to explain that:
Suppose the CDs said, "all interior doors shall be painted red, primer + 2 coats semigloss latex". You do it because that was stated on the plans that were referenced your contract. You might send an RFI saying "what color red?", or "how thick are the coats?" But there is little question that you need to paint the doors, because it is in the contract.
However, if the CDs said "interior door finish of all doors shall comply with the California Building Code", then you don't need to paint the doors at all, because the California Building Code does not require interior doors to be painted.
*
In this case the CBC does not require accessible closet pull tabs. In fact, it probably doesn't require any door hardware at all at the closets.
It is possible that the original poster's problem might not be that cup pulls were installed in lieu of ADA pulls; the problem (if the owner were to play this game) might be that hardware pulls were installed if/when none were called out on the plans. The owner could say, "hey, you ruined my perfectly smooth flat closet doors by cutting holes in them to install hardware that the CDs did not ask for. Fix it, or give me a credit". Now, if the architect directed the contractor to install cup pulls, then the contractor may have recourse to removing the cups and patching the doors.
 
Anyone read 1126A.6 Hand-Activated Door or gate hardware? What good is it to provide a door if you can't open it?
Door hardware in this case is an element of the new construction. It has not risen to the level of accommodation.
Did the project have specifications separate from the DWG's? Did the owner signoff on them?
Could have used bifolds in lieu of sliding and "U" pulls could have been specified.
Yes the project is not under ADA, it is under FHA HUD and CBC except for any public use spaces (leasing office, community room, etc.) which are.
This could have been caught early on but now the owner is making a mountain out of a molehill.
Did the developer have prior experience, own many units?
 
Anyone read 1126A.6 Hand-Activated Door or gate hardware? What good is it to provide a door if you can't open it?

1126A.6 is part of Section 1126A, which is in Div. III - "Building Features". This is for areas outside of the dwelling unit, or as 1126A.1 puts it, for "doorways which provide access to common use areas or multifamily dwellings".

Once you are inside the dwelling unit, Division IV "Dwelling Unit Features" takes over, including section 1132A for doors.
1132A.2 says "interior doors intended for user passage and secondary exterior doors shall comply with THIS section" - - more proof that 1126A is not applicable inside a dwelling unit.
Furthermore, as per post #3, a shallow clothes closet (less than 4' deep, which is the designed wheelchair depth) is not intended for "passage", so even section 1132A.2 doesn't apply in that particular situation. It gets treated like the door on a kitchen cabinet in CBC 11A - - no hardware required.
So yes, inside the dwelling unit, cup hardware has risen to the required level of accommodation, because no accommodation is required by applicable codes or regulations.

To answer your question, "what good is it to provide a door if you can't open it?", their are plenty of people who can pull or drag a sliding closet door with their fingers, whether with a cup pull or even with no pull at all. At home, I have a bedroom closet with sliding doors and no pulls at all. The hardware glides are so smooth that the minor friction of your palm or fingers on the door face is enough to slide it open.
You might ask, "but what about the tenant that has no fingers, using a closet door that does not glide so easily?". See the FHA answer in post #5: that tenant can always make their own post-construction "reasonable accommodation" request to the owner.

Remember, the problem in the original post is that the owner is claiming the contractor is on the hook to provide ADA pulls for free because the code or other applicable regulations require it, even though the plans didn't call for it. I challenge anyone to cite anywhere in the scope of CBC 11A or FHA where a regulation applicable to privately funded housing requires (not merely "recommends") accessible door pulls on non-passage clothes closets inside a private covered multifamily dwelling unit.
I can't find it.

Can you?
 
Last edited:
accepted: 2020 FHA Design manual differs to ANSI 4.13 Req. 3
"2020 FHA Design manual" - HUD still shows the 1998 version on its website. Do you have a link to this document?

Also, to which ANSI standard edition are you referring? Several editions are considered safe harbors, which means that if the safe harbor differs from the Design Manual, then complying with the safe harbor document is all that is necessary (unless the FHA Design Manual is specifically included by reference).
 