• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Handrail extensions and landing depth

pmarx

Bronze Member
Joined
Oct 13, 2010
Messages
114
This is for the 2009 IBC. At the bottom of a stair where the handrail is no longer continuous and must either return to the floor, wall or guardrail, does the one tread extension now define the landing depth? For example, if the stair width is 44" then the landing must be 44" deep. Does the handrail extension on the open side of a stair reduce the landing to 44" minus the extension? The stair enclosure is 96" wide, not 44".
 
It depends on where the egress doorway is located.

If the door is located directly ahead from the last step, then the 44 inches is measured from the last riser to the door. However, per ANSI A117.1, you need 48 inches of depth for maneuvering clearance for a forward approach on push side, so the depth of the landing will require 48 inches. Plus, since the door will have a closer and a latch, you need 12 inches of clearance on the latch side. This would place the handrail extension inside of the maneuvering clearance, so the 48-inch-deep clearance would be measured from the end of the handrail extension.

The door can be placed on the same wall, but inline with the other side of the stair, making for a side approach on the push side of the door. Since the door has a closer and latch, the width of the maneuvering clearance is also required to be 48 inches, so the handrail extension would have to be outside of that clearance.

If the door is on the wall facing the open side of the stair, that would allow a forward approach, too. At 48 inches in depth, this would probably clear the handrail extension since the width of the enclosure is 96 inches. The landing can be the 44 inches measured from the last riser, which would provide the minimum accessible width of 32 inches clear (44 inches minus 12 inches of handrail extension), but would not provide the minimum width of 44 inches for means of egress (39-1/2 inches of clear width with 4-1/2 inches of permitted handrail extension into the required egress width). Thus, the depth of the landing would need to be 51-1/2 inches.

The door can be on the wall on the stair side of the enclosure, but the landing would need to provide for the width of the door plus 24 or 22 inches, depending on which side of the door the latch is located. It would also require 48 inches of width because of the closer and latch, which may cause the handrail extension on the open side to encroach into the maneuvering clearance.
 
It depends on where the egress doorway is located.

If the door is located directly ahead from the last step, then the 44 inches is measured from the last riser to the door. However, per ANSI A117.1, you need 48 inches of depth for maneuvering clearance for a forward approach on push side, so the depth of the landing will require 48 inches. Plus, since the door will have a closer and a latch, you need 12 inches of clearance on the latch side. This would place the handrail extension inside of the maneuvering clearance, so the 48-inch-deep clearance would be measured from the end of the handrail extension.

The door can be placed on the same wall, but inline with the other side of the stair, making for a side approach on the push side of the door. Since the door has a closer and latch, the width of the maneuvering clearance is also required to be 48 inches, so the handrail extension would have to be outside of that clearance.

If the door is on the wall facing the open side of the stair, that would allow a forward approach, too. At 48 inches in depth, this would probably clear the handrail extension since the width of the enclosure is 96 inches. The landing can be the 44 inches measured from the last riser, which would provide the minimum accessible width of 32 inches clear (44 inches minus 12 inches of handrail extension), but would not provide the minimum width of 44 inches for means of egress (39-1/2 inches of clear width with 4-1/2 inches of permitted handrail extension into the required egress width). Thus, the depth of the landing would need to be 51-1/2 inches.

The door can be on the wall on the stair side of the enclosure, but the landing would need to provide for the width of the door plus 24 or 22 inches, depending on which side of the door the latch is located. It would also require 48 inches of width because of the closer and latch, which may cause the handrail extension on the open side to encroach into the maneuvering clearance.

Thanks for the reply. I wish I could have figured out how to attache a .pdf (if that's possible) to illustrate the condition. There isn't a conflict with a door. I'm just not sure if the handrail extension must be considered as a reduction to the landing.
 
Thanks for the reply. I wish I could have figured out how to attache a .pdf (if that's possible) to illustrate the condition. There isn't a conflict with a door. I'm just not sure if the handrail extension must be considered as a reduction to the landing.
The simple answer is 'no'; the handrail extension does not reduce the landing depth anymore than the 12-inch extension does to the landing at the top of the stair. However, the 44-inch landing you described will probably not comply with the various maneuvering clearances depending on the egress door location.
 