• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Mechanical Room wall rating - 2018 IMC

redbird11

SAWHORSE
Joined
Apr 10, 2018
Messages
45
Location
Over the rainbow
2018 International Mechanical Code, Section 602 - Plenums allows mechanical rooms to be used as an air plenum. What it doesn't clearly state is whether the mechanical room walls need to be rated? The adjacent shaft will be 2 hour.
 
I think you'd find such requirements in the IBC, not the IMC. For example the requirements of the shaft are in 713. I don't think there's a simple answer to your question, because it begs questions involving rated corridors and the like. I don't think there is a requirement on the mechanical room itself, but I could be missing something...
 