Many of our projects are tall enough and use the "right" combination of materials to require NFPA 285 compliance. NFPA 285 test assemblies typically are built with gyp board fitting tightly to the slab above within the test chamber. Many projects in the real world don't have a nice clean flat slab condition that allows board to be installed tight to the underside. Most of our projects are steel frame construction, with a spandrel beam parallel to the exterior wall and a few inches in from the light gauge metal framing, making fastening of the gyp board above the bottom flange of the beam and installation of a second gyp bd cover over a deflection track nearly or completely impossible. That means a gap of undetermined size in the interior gypsum board type X finish...which could be seen as compromising the tested assembly. I'm polling what the general practices other firms use to deal with this:
- Extend the gyp board as high as it can be fastened (i.e. bottom of beam) and don't worry about the rest since the test deals with flame propagation up the outside of the wall
- Extend the gyp board as high as it can be fastened, and fill (in some manner) the stud cavities above or out to the beam with mineral wool insulation or some type of firestopping spray (assuming this is NOT balloon framing)
- Extend the gyp board full height, and fasten as high as you can, leaving the spandrel condition next to the beam unfastened and untaped/unmudded
- Construct a soffit around the spandrel beams with type X gyp board to provide continuity to the underside of deck on the interior side of the beam, with or without firestopping of penetrations.
- Move all steel framing farther away from the outside wall to provide sufficient space to get in there and get it done, thereby adding additional steel cost for outriggers and slab edge support.
- Use all noncombustible materials in the exterior wall assembly to negate NFPA285 requirements.
- Build everything with CMU.