Testing Generator Sizing Calculator - Need Help Testing

I recently wired a piece of industrial equipment with a 350hp motor and a 50hp motor.
So that's 465A or 386 kVa. I'm currently running this off a 500 kw generator. No problem right?

My 500 kw generator workes out to 602A. Now here is why motors are of concern.

The 350 HP motor is on a soft starter. It draws 1604A for 10 seconds before soft start bypass engages and the motor draws 401A.
Generators have to have the "balls" to start these kinds of loads.
 
The 350 HP motor is on a soft starter. It draws 1604A for 10 seconds before soft start bypass engages and the motor draws 401A.
Generators have to have the "balls" to start these kinds of loads.
I think that is a conversation to have with the generator manufacturer based on that fact. Sizing a generator is rather straightforward until you have an issue like this. It sounds to me like this motor should be on a VFD to reduce the inrush current and not just a soft start. Or, you can adjust that soft start. That is too much current for a motor with a soft start.
 
I think that is a conversation to have with the generator manufacturer based on that fact. Sizing a generator is rather straightforward until you have an issue like this. It sounds to me like this motor should be on a VFD to reduce the inrush current and not just a soft start. Or, you can adjust that soft start. That is too much current for a motor with a soft start.
I would agree VFD makes for a better choice considering the size.
 