  1. jar546

    NEC 334.15(B) Chris Kennedy Code Change 2023 NEC

    The undisputed King of Romex, our own Chris Kennedy is sponsoring this 2023 NEC Code Change. (B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC...
  2. jar546

    90°C Wire for Feeder

    So here is the scenario. Would you allow this setup? An 800A MDP (with service disconnect) has to feed a panelboard with a total load of 400A which includes continuous and non-continuous loads. The breaker in the MCP has 75°C terminals as expected and so do the lugs in the panelboard it will...