Michigan Building Code 2015. Vb construction fully fire suppressed. Apartments. We only need a 1/2 hour rating on the separation between corridor and apartment.
We have an issue where they have installed the tub enclosure of the apartment on the corridor wall. There is no drywall behind it so only the corridor side has gyp. We are trying to use section 722 of calculated fire resistance that we can use 1 layer of 5/8" gyp board which has a 30 minute rating on the corridor side. That would make a 1/2 hour separation between the two. We will even double it if it helps.
Inspector is saying we need to protect from both sides.
Is there any section I can look at that says what side of the partition needs the protection? These are non-load bearing interior walls. I know there is a National Gypsum (2) layer asymetrical rated wall, but its metal stud. Which is why im trying to look at the "calculated fire resistance" since we are under 1 hour required separation.
We have an issue where they have installed the tub enclosure of the apartment on the corridor wall. There is no drywall behind it so only the corridor side has gyp. We are trying to use section 722 of calculated fire resistance that we can use 1 layer of 5/8" gyp board which has a 30 minute rating on the corridor side. That would make a 1/2 hour separation between the two. We will even double it if it helps.
Inspector is saying we need to protect from both sides.
Is there any section I can look at that says what side of the partition needs the protection? These are non-load bearing interior walls. I know there is a National Gypsum (2) layer asymetrical rated wall, but its metal stud. Which is why im trying to look at the "calculated fire resistance" since we are under 1 hour required separation.