• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

1/8" slope on walkable surface?

gnarkill283

Registered User
Joined
Nov 15, 2017
Messages
107
Location
New York
We have a stamped concrete deck on a roof with drains (and emergency overflow drains) flush with the concrete finish. The slope to the drains is no greater than 1/4" (to a foot) since its a walkable surface and no less than 1/8" since that is the minimum for drainage. We are receiving comments that 1/8" is too little of a slope for drainage and 1/2" should be maintained. First off 1/2" doesn't meet ada cross slope requirements of 1:48 or 2% max and how would one maintain 1/2" throughout a large deck that is not perfectly square? If 1/2" is maintained, the top of slope to some drains will be higher than others and you can't have bump ups on a walkable surface. Appreciate any help - thanks
 
The least slope of the various roof covering types is 1/8" per foot. If the concrete roof covering is being done after the fact and would qualify as a re-roof, there is no minimum slope required as long as the roof drains.
 
The least slope of the various roof covering types is 1/8" per foot. If the concrete roof covering is being done after the fact and would qualify as a re-roof, there is no minimum slope required as long as the roof drains
This is all new construction
 
Is this a slab poured over a waterproofing membrane? If so, there should be subslab drainage at the membrane as well (similar to a shower drain detail). Emergency overflow drains should be a couple inches above the slab.
 
Is this a slab poured over a waterproofing membrane? If so, there should be subslab drainage at the membrane as well (similar to a shower drain detail). Emergency overflow drains should be a couple inches above the slab.
Yes - the emergency drains are spaced away from the main drain following the slope - how far would it have to be to meet code? If the slope is 1/8" then 8' away would mean its an inch higher than the main drain - is that enough height difference?
 
When i was in high rise construction about a hunnert years ago, we poured a porous concrete surface over a waterproof membrane on the roof of the building. I don’t remember the details, but the concrete batch plant came up with the mix design. We poured a 2x2 ft sample for the customer to approve, put it on saw horses so we could pour a bucket of water through it while they used a stop watch to calculate the porosity. Surprised everybody, the water ran through the concrete like it wasn’t there.
 
1/8" per foot roof slope used to be typical. The codes increased it to 1/4" sometime in the 1990s, probably because roof deflections would cause water to puddle on a 1/8" slope. I don't know of any code requirement for a 1/2" slope. It would be best to try to get a 1/4" slope to minimize the chance of puddles which could freeze in the winter and cause a slipping hazard for people.
 