IBC Sec 705.5 The required fire-resistance rating of an exterior wall with a fire separation distance greater than 10 feet shall be rated for exposure from the inside.
Would this indicate the protection at the interior side of the wall is 5/8" type X, and the protection at the exterior side of the wall is omitted?
Can I reference something like UL #U309 as the fire test?
This is a sprinklered building with R-2 occupancy and type V-A construction.
Sprinkler used to increse allowed building height from 3 stories to 4 stories.
Table 601: Type V-A exterior walls= 1 hour rated
Table 602: X>30', all types of construction, R-2 Occupancy= 0
Would this indicate the protection at the interior side of the wall is 5/8" type X, and the protection at the exterior side of the wall is omitted?
Can I reference something like UL #U309 as the fire test?
This is a sprinklered building with R-2 occupancy and type V-A construction.
Sprinkler used to increse allowed building height from 3 stories to 4 stories.
Table 601: Type V-A exterior walls= 1 hour rated
Table 602: X>30', all types of construction, R-2 Occupancy= 0