Bootspurs
REGISTERED
Context is a remodel of an existing 2-story single family home into an upstairs/downstairs duplex, in California. Code calls for 1 hour separation between dwellings, plus a 1 hour rating on all exterior walls on the lower floor walls that support the one-hour floor ceiling assembly. CRC section R302.3 provides an exception to the 1-hour fire requirement as follows:
A fire-resistance rating of 1/2 hour shall be permitted in buildings equipped throughout with an automatic sprinkler system installed in accordance with NFPA 13.
I’m the owner and am getting pushback from city contracted plan reviewed that this exception applies only to NFPA 13 fire sprinkler systems (which are used in commercial buildings), and therefore this exception doesn’t apply to NFPA 13R systems, which are what are used in most residential fire sprinkler systems.
Is there any basis for this? Wouldn’t any sprinkler system (NFPA 13/13R/13D) meet this intent of putting out a fire before the 1 hour rating would have been needed? I’ve found some AHJs that reference any sprinkler system that meets P2904, but nothing in California.
Fire sprinklers weren’t even required but I’d rather install them then take off all the siding to make the exterior walls 1-hour rated; I thought that exception would make that approach possible.
I’ll also note that this needs STC rating > 45 as well, and it has existing 2x6 ceiling joists. It’s an old house and would be best if I didn’t have to tear open ceilings and upstairs floors to get the STC rating.
City says both fire and STC rating must be listed assemblies.
I’ve found at least one similar cases described on this forum, but it wasn’t quite conclusive on what was finally accepted. Thanks for any ideas on how to proceed.
A fire-resistance rating of 1/2 hour shall be permitted in buildings equipped throughout with an automatic sprinkler system installed in accordance with NFPA 13.
I’m the owner and am getting pushback from city contracted plan reviewed that this exception applies only to NFPA 13 fire sprinkler systems (which are used in commercial buildings), and therefore this exception doesn’t apply to NFPA 13R systems, which are what are used in most residential fire sprinkler systems.
Is there any basis for this? Wouldn’t any sprinkler system (NFPA 13/13R/13D) meet this intent of putting out a fire before the 1 hour rating would have been needed? I’ve found some AHJs that reference any sprinkler system that meets P2904, but nothing in California.
Fire sprinklers weren’t even required but I’d rather install them then take off all the siding to make the exterior walls 1-hour rated; I thought that exception would make that approach possible.
I’ll also note that this needs STC rating > 45 as well, and it has existing 2x6 ceiling joists. It’s an old house and would be best if I didn’t have to tear open ceilings and upstairs floors to get the STC rating.
City says both fire and STC rating must be listed assemblies.
I’ve found at least one similar cases described on this forum, but it wasn’t quite conclusive on what was finally accepted. Thanks for any ideas on how to proceed.