• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

100 KAIC panel for a 62 KAIC service?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
3,075
Location
Southern California
The dept of water and power said they will supply my 1600 amp apartment switchgear (208Y, 120V, 3 phase, 4 wire) with a max fault current of 62KAIC. The motor contribution brings it up to 63.66 KAIC.

We originally spec'd a 65 KAIC panel, but the plan checker is saying we must provide a 100KAIC panel, for an additional factor of safety. Can he legitimately require something that goes beyond the requirements of the DWP and the engineer of record, and the calculated loads? If so, why?

At this stage of the project, we can't afford the switchgear upcharge, nor the opportunity for supplier to revisit their price quote.
 
I say no. There is no "additional factor of safety" section of the NEC. The 65K equipment satisfies Section 110.9 of the NEC. No "additional" considerations are needed. The maximum possible fault current cannot and will not exceed 65,000 amperes so equipment with a higher rating is not necessary and will serve no purpose...
 
I agree with Bryan, there is no safety factor required by the NEC. 110.9 requires the AIC rating of the equipment to meet or exceed the available fault current.

Chris
 
Yikes said:
The dept of water and power said they will supply my 1600 amp apartment switchgear (208Y, 120V, 3 phase, 4 wire) with a max fault current of 62KAIC. The motor contribution brings it up to 63.66 KAIC.
I certainly agree with Bryan and Chris that this is not an NEC issue.

I do find this odd though. Here for a service as mentioned, POCO would supply tranny specs and a primary at infinity. They don't do secondary fault current calcs for us. 62K seems high to me unless the tranny is sitting on top of your service gear. So I question have your done your own calc on this? Could be an option to expedite this through plans review.
 