1007.8 ibc 2009

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
comments?? pro con enforcing it??? how???

1007.8 Two-way communication. A two-way communication

system shall be provided at the elevator landing on each

accessible floor that is one or more stories above or below the

story of exit discharge complying with Sections 1007.8.1 and

1007.8.2.

Exceptions:

1. Two-way communication systems are not required at

the elevator landing where the two-way communication

system is provided within areas of refuge in

accordance with Section 1007.6.3.

2. Two-way communication systems are not required on

floors provided with exit ramps

section heading

1007.1 Accessible means of egress required. Accessible

means of egress shall comply with this section. Accessible

spaces shall be provided with not less than one accessible

means of egress. Where more than one means of egress are

required by Section 1015.1 or 1021.1 from any accessible

space, each accessible portion of the space shall be served by

not less than two accessible means of egress.
 