• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

1008.1.4.4 and 1008.1.9.8 ibc 2009

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
Thanks to Lori and her comapny for the fantastic book that was put out on doors, if you have not gotten one yet, very good reading.

Sorry do not have the sections to publish

they both deal with access controlled egress doors

the first section is for entance doors, and the other is for doors in the means of egress

as I saw on another forum it seems like the code books are getting bigger, in order to deal with special situations

in this case one section is entrance doors, and it allows you to use a push button, and the other section is for doors in the means of egress, which does not allow the push button, but requires listed hardware on the door to relase the magnet.

just wonder why the need for two sections, and why they cannot match????

not a push button near the door fan.
 
Last edited by a moderator:
Here are the code sections for you

1008.1.4.4 Access-controlled egress doors.

The entrance doors in a means of egress in buildings with an occupancy in Group A, B, E, I-2, M, R-1 or R-2 and entrance doors to tenant spaces in occupancies in Groups A, B, E, I-2, M, R-1 and R-2 are permitted to be equipped with an approved entrance and egress access control system which shall be installed in accordance with all of the following criteria:

1. A sensor shall be provided on the egress side arranged to detect an occupant approaching the doors. The doors shall be arranged to unlock by a signal from or loss of power to the sensor.

2. Loss of power to that part of the access control system which locks the doors shall automatically unlock the doors.

3. The doors shall be arranged to unlock from a manual unlocking device located 40 inches to 48 inches (1016 mm to 1219 mm) vertically above the floor and within 5 feet (1524 mm) of the secured doors. Ready access shall be provided to the manual unlocking device and the device shall be clearly identified by a sign that reads "PUSH TO EXIT." When operated, the manual unlocking device shall result in direct interruption of power to the lock-independent of the access control system electronics-and the doors shall remain unlocked for a minimum of 30 seconds.

4. Activation of the building fire alarm system, if provided, shall automatically unlock the doors, and the doors shall remain unlocked until the fire alarm system has been reset.

5. Activation of the building automatic sprinkler or fire detection system, if provided, shall automatically unlock the doors. The doors shall remain unlocked until the fire alarm system has been reset.

6. Entrance doors in buildings with an occupancy in Group A, B, E or M shall not be secured from the egress side during periods that the building is open to the general public.

1008.1.9.8 Electromagnetically locked egress doors.

Doors in the means of egress that are not otherwise required to have panic hardware in buildings with an occupancy in Group A, B, E, M, R-1 or R-2 and doors to tenant spaces in Group A, B, E, M, R-1 or R-2 shall be permitted to be electromagnetically locked if equipped with listed hardware that incorporates a built-in switch and meet the requirements below:

1. The listed hardware that is affixed to the door leaf has an obvious method of operation that is readily operated under all lighting conditions.

2. The listed hardware is capable of being operated with one hand.

3. Operation of the listed hardware releases to the electromagnetic lock and unlocks the door immediately.

4. Loss of power to the listed hardware automatically unlocks the door.
 
mine is more of a minor rant than a question

why keep adding sections to the code when you can modify existing.

why can't common code section be put together, instead of hunting, such as these two

and like I said not a push button fan
 