Here's the situation: We have a four-story Type IIIB condo building under the 2015 IBC. Elevator served, with two interior exit stairs.
The top floor is the fourth story, which has two main types of spaces on it:
1. Enclosed residential spaces that are only the upper stories of multi-story dwelling units that have their accessible entries and spaces on the third story, and
2. A shared roof deck amenity, 100% open to the sky, with zero enclosed space. The roof deck is served by the stairs and the elevator.
The 2015 IBC text says "1009.2.1 Elevators required. In buildings where a required accessible floor is four or more stories above or below a level of exit discharge, not less than one required accessible means of egress shall be an elevator complying with Section 1009.4."
One of the exit stairs discharges at a basement level, so our fourth story is definitely "four ... stories above or below a level of exit discharge."
Does our required accessible roof deck trigger the need for an elevator with standby power for 1009.4?
I think it doesn't because:
1. The only real fourth story interiors are the not-accessible upper halves of the multistory dwelling units,
2. If the roof deck were on its own at this fourth story level (i.e., not sharing this level with the enclosed unit spaces), it clearly would not trigger 1009.2.1, because it would not be a story.
Am I wrong?
The challenge here is that we'd need a generator for standby power, and that is hard to work in on our site. Not to mention that it'd cost $.
Thanks for any opinions or guidance!
The top floor is the fourth story, which has two main types of spaces on it:
1. Enclosed residential spaces that are only the upper stories of multi-story dwelling units that have their accessible entries and spaces on the third story, and
2. A shared roof deck amenity, 100% open to the sky, with zero enclosed space. The roof deck is served by the stairs and the elevator.
The 2015 IBC text says "1009.2.1 Elevators required. In buildings where a required accessible floor is four or more stories above or below a level of exit discharge, not less than one required accessible means of egress shall be an elevator complying with Section 1009.4."
One of the exit stairs discharges at a basement level, so our fourth story is definitely "four ... stories above or below a level of exit discharge."
Does our required accessible roof deck trigger the need for an elevator with standby power for 1009.4?
I think it doesn't because:
1. The only real fourth story interiors are the not-accessible upper halves of the multistory dwelling units,
2. If the roof deck were on its own at this fourth story level (i.e., not sharing this level with the enclosed unit spaces), it clearly would not trigger 1009.2.1, because it would not be a story.
Am I wrong?
The challenge here is that we'd need a generator for standby power, and that is hard to work in on our site. Not to mention that it'd cost $.
Thanks for any opinions or guidance!