1013.5 Mechanical equipment.
Guards shall be provided where appliances, equipment, fans, roof hatch openings or other components that require service are located within 10 feet (3048 mm) of a roof edge or open side of a walking surface and such edge or open side is located more than 30 inches (762 mm) above the floor, roof or grade below. The guard shall be constructed so as to prevent the passage of a sphere 21 inches (533 mm) in diameter. The guard shall extend not less than 30 inches (762 mm) beyond each end of such appliance, equipment, fan or component.
New construction HVAC equipment is within 7 feet of a lower level roof. The distance between the two different roof surfaces is 28 inches. However the 8 inch wide by 12 inch high parapet that separates the two levels is the question the Architect has.
He states the 30 inches is measured from roof surface to roof surface because that is the distance a person will fall.
That's logical but I am not sure that is the intent of the code. The 12 inch parapet could be viewed as a tripping hazard but the mechanical code only requires a 30" X 30" level working surface so it is outside of the required clearances. In reality there are all kinds of tripping hazards on a roof.
Where would you measure the distance from?
1. Surface to surface?
2. Top of the parapet to the lower roof surface?
Guards shall be provided where appliances, equipment, fans, roof hatch openings or other components that require service are located within 10 feet (3048 mm) of a roof edge or open side of a walking surface and such edge or open side is located more than 30 inches (762 mm) above the floor, roof or grade below. The guard shall be constructed so as to prevent the passage of a sphere 21 inches (533 mm) in diameter. The guard shall extend not less than 30 inches (762 mm) beyond each end of such appliance, equipment, fan or component.
New construction HVAC equipment is within 7 feet of a lower level roof. The distance between the two different roof surfaces is 28 inches. However the 8 inch wide by 12 inch high parapet that separates the two levels is the question the Architect has.
He states the 30 inches is measured from roof surface to roof surface because that is the distance a person will fall.
That's logical but I am not sure that is the intent of the code. The 12 inch parapet could be viewed as a tripping hazard but the mechanical code only requires a 30" X 30" level working surface so it is outside of the required clearances. In reality there are all kinds of tripping hazards on a roof.
Where would you measure the distance from?
1. Surface to surface?
2. Top of the parapet to the lower roof surface?