Keystone
SAWHORSE
Who has used this allowance and in what circumstance?
so a modification???AegisFPE said:We're often able to stay within the alternate means and methods provision. However, that requires the material or method to at least be "equivalent" to the protection prescribed by the code.When the protection prescribed by the code cannot be achieved, we develop a plan that satisfies the intent of the code. In such cases the design approach cannot be said to be equivalent to the prescribed provision, but can be considered to provide the intended level of protection.
NFPA 101, 2000
4.6.1.3
Where it is evident that a reasonable degree of safety is provided, any requirement shall be permitted to be modified if its application would be hazardous under normal occupancy conditions in the judgment of the authority having jurisdiction.
4.6.3* Modification of Requirements for Existing Buildings.Where it is evident that a reasonable degree of safety is provided, the requirements for existing buildings shall be permitted to be modified if their application would be impractical in the judgment of the authority having jurisdiction.
1.5.1*
The specific sections for modifications were just moved out of Chapter 1 to the General sections of Chapter 4 with the equivalency criteria remaining in the administrative chapter.Nothing in this Code is intended to prevent the use of systems, methods, or devices of equivalent or superior quality, strength, fire resistance, effectiveness, durability, and safety over those prescribed by this Code. Technical documentation shall be submitted to the authority having jurisdiction to demonstrate equivalency. The system, method, or device shall be approved for the intended purpose by the authority having jurisdiction.