Greetings all,
When I passed my Houston and Pasadena masters tests 20 some odd years ago I said I wasn't ever going to test in the NEC again. Killed too many brain cells.
Well, times change.
I'm trying to figure out the meaning of the last sentence in the referenced section. 110.14©
"Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."
So, if a THHN conductor (rating 90 degree C) is being used in conjuntion with a 60 degree C terminal, may the ampacity from the 90 degree C colum be used to derate for excessive temperature or # of current carrying conductors over 3? Or, is this just a redundant statement and it allows me to use a conductor temperature with a higher temperature rating but utlilizing the ampacity of the colum that corresponds to the terminal temp rating?
Thanks
BS
When I passed my Houston and Pasadena masters tests 20 some odd years ago I said I wasn't ever going to test in the NEC again. Killed too many brain cells.
Well, times change.
I'm trying to figure out the meaning of the last sentence in the referenced section. 110.14©
"Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."
So, if a THHN conductor (rating 90 degree C) is being used in conjuntion with a 60 degree C terminal, may the ampacity from the 90 degree C colum be used to derate for excessive temperature or # of current carrying conductors over 3? Or, is this just a redundant statement and it allows me to use a conductor temperature with a higher temperature rating but utlilizing the ampacity of the colum that corresponds to the terminal temp rating?
Thanks
BS