11B vs Chapter 10 visual alarm disconnect

ADAguy

REGISTERED
Joined
Sep 11, 2013
Messages
6,307
Location
California
If you provide a audible/visual fire alarm as required by Chapter 10, how are verbal alarm communications conveyed to a deaf person?

This can/could be accomplished by use of a captioning device but is one required? (You are required to provide the alarm system but no mention is made of captioning in 10) Is the device a sign? If so, must it comply with visual display board requirements in Chapter 11B-703.8?
 
I don't have a copy here but, I do not think the NFPA 72, the National Fire Alarm and Signaling Code has a captioning device listed as a audible/visual fire alarm
 
Have not heard that it is required

Unless a California thing, than the problem would it be through out a building??
 
Ok looking at the 2015 ibc

F] 907.5.2.2.4 Emergency voice/alarm communication captions.

Where stadiums, arenas and grandstands are required to caption audible public announcements in accordance with Section 1108.2.7.3, the emergency/voice alarm communication system shall be captioned. Prerecorded or live emergency captions shall be from an approved location constantly attended by personnel trained to respond to an emergency.
 
Only for stadiums as indicated. DOJ has also issued a letter basicly saying the same thing until such time as it is required by NFPA. Seems to overlook the needs of those with hearing loss.
 
Well, I don't pay attention all the time

If I see a large crowd leaving either the game is over or there is a problem and I should follow the herd
 