• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

120/208 3 phase to condo and apartment buildings

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,051
Location
Somewhere Too Hot & Humid
Honest question that I don't know.

What, in most cases is the single, largest factor for deciding to run 120/208 3 phase instead of 120/240 single phase to an apartment building or condo setup?

I am especially curious when the house panel does not run much other than lighting and other small common area circuits.
 
By running a 3 phase service to those buildings you can install a smaller service then if you used a single phase service. That is the biggest factor I have seen for the decision to run a 120/208 3 phase service instead of a 120/240 single phase service.

So for example I have a calculated load of 200 Kva for simplicity sake.

200,000 divided by 240 would result in a single phase service of 833.333 amps or more likely a 1,000 amp service.

200,000 divided by 208*1.732 (Square root of 3) would result in a 3 phase service size of 555.555 or more likely a 600 amp service.

Chris
 
I was confused by this because some POCOs charge significantly more for 3 phase services and in this case I did not know if the reduction in service size paid for the additional costs of a 3 phase service. About 2 years ago we had a lot of permits to convert 3 phase services back to single where they did not have any equipment that needed 3 phase.

Thanks for the clarification.
 