• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

13D backflow preventers

retire09

Silver Member
Joined
Feb 19, 2010
Messages
365
Location
Alaska
Does a 13D stand alone wet system with no anti freeze require the installation of a back flow preventer?

I am told that they do, but the only requirement I can find in 13D involves antifreeze.

Can anyone give me a reference section in 13D?
 
My 2007 13D does not require backflow protection - however the Annex (explanatory info) advises that backflow and metering is subject to local regulation, and a diagram indicates a "rubber faced check valve" as being optional.
 
none required. some ahj will require the system to have a loop that would hook up to a water closet to keep the water from stagnation.
 