Given:
2018 IBC is the applicable code. More specifically section 2603.4. A 15 minute thermal barrier is required to separate the foam plastic insulation from the interior of the building.
The foam insulation on the walls is covered with 5/8" gypsum board. But this drywall extends only a few inches above the lay-in ceiling.
Questions:
1) Is it possible to specify the one-hour fire-rated lay-in ceiling that would meet the intent of this requirement?
2) If not, then is it possible to apply a coat of intumescent paint to the exposed foam insulation?
As always, thanks in advance.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner