• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

1995 CABO ?

mtlogcabin

SAWHORSE
Joined
Oct 17, 2009
Messages
9,484
Location
Big Sky Country
What was the bollard spacing for guardrails in the 95 Cabo edition. 92 was 6". I need to know if Cabo ever went to the 4" requirement.
 
Re: 1995 CABO ?

Guard openings = 4"

Triangular openings formed by the riser, tread and bottom rail of a guard = 6"
 
Re: 1995 CABO ?

1992 Cabo R-214.2

Required guardrails on open sides of stairways, raised floor areas, balconies and porches shall have intermediate rails or ornamental closures which shall not allow passage of an object 6 inches or more in diameter. I thought his applied to the bollards

Horizontal spacing between the vertical members in required guardrails shall be a maximum of 4 inches at the nearest point between members. This would be the space from the floor to the bottom rail of the bollards. Am I correct or do I have it wrong. One requirement is a 6" diameter the other is a 4" measurment
 
Re: 1995 CABO ?

I think the two requirements conflict. I would interpret as 4" between bollards/spindles/vertical members. Others may or may not have the same interpretation. Good thing it is an outdated code.
 
Re: 1995 CABO ?

Good thing it is an outdated code.
I agree my problem is home built under 95 Cabo which city inspected and child got caught between the bollards last week so the finger pointing has started. Rental duplex owned by an attorney.
 
Re: 1995 CABO ?

Ah, CABO. The good old days. MT, I have CABO in my personal library back to 76. But it is still in boxes. CABO a long time ago was 6" spacing. I'll nail down the year tomorrow when they went to 4".

"Good thing it is an outdated code." I have to take exception to that. It was an excellent code written by all three of the model code organizations. SBCCI, BOCA, ICBO. Perscriptive in nature and a heck of a lot easyer to enforce.
 
Re: 1995 CABO ?

JP stated,

"Good thing it is an outdated code." I have to take exception to that. It was an excellent code written by all three of the model code organizations. SBCCI, BOCA, ICBO. Perscriptive in nature and a heck of a lot easyer to enforce.

I too started this job under CABO and preferred it to the combined thing we have now. BUT, the section being referenced by M&M and MT is confusing at best in the "92" edition.
 
Re: 1995 CABO ?

The CABO code isn't outdated. The IRC is just the CABO code with a ton of seismic and hurricane requirements added.

The CABO code actually was tougher than the 2006 IRC. R312.2 now allows 4 3/8" clear between balusters, so that two tapered balusters can be used for each tread, instead of having to go to 3 balusters per tread.

The exception to allow a 6" sphere to pass below the bottom member of a stair rail is there because the bottom member would have to be below the nosing line to keep a 4" sphere from passing.
 
Re: 1995 CABO ?

steveray already gave the correct answer, but here is the language verbatim.

315.4 Guardrail opening limitations.

Required guardrails on open sides of stairways, raised floor areas, balconies and porches shall have intermediate rails or ornamental closures which do not allow passage of an object 4 inches (102 mm) or more in diameter.

Exception: The triangular openings formed by the riser, tread and bottom rail of a guard at the open side of a stairway may be of such a size that a sphere 6 inches (153 mm) cannot pass through.
 
Re: 1995 CABO ?

Thanks every one. The bollards are in an interior stair and they exceed the 4" requirement but do not exceed the 4 3/8" allowed under today's code. Attorney (she devil with a tie) wants me to cite the contractor and make him replace the bollards at the CABO 4" requirement. :roll: Told her I could not cite him because it is code compliant under todays code but. Went away grumbling about the Building Department not wanting to do their job. Made my week ;)
 
Top