1hr rated electrical room door rating
ennisdavis
tampa
So I have an electrical room, no transformer, 1hr rating, and the door does not go into an exit corridor, Is the door rating 45 or 60 minutes?
What kind of business??
Where is the room
Inner room off another
In a storeroom or something
Ok should have asked
Existing, new or proposed building
IBC or NFPA 101 in play?
Not necessarily .....What is the exact code reference for requiring the electrical room to be rated for one hour? Exception to NFPA 13 = 2 hour, Smoke Control room = 1 hour, etc.
IS this an elevator equipment room? Then the 1 hour fire rated wall(s) is a fire barrier (and/or ceiling) with a 60 min. door (opening protective) required.
Our code permits the rating of a door to be lower than the wall it is located in. This is based on the assumption that there is unlikely to be a fire load directly adjacent to a door. In most cases, a 1 hour wall only requires a 45 minute door here in Canada.
Not sure I have enough info?
2012 IBC Table 716.5, Exterior walls with a 1-HR rating, MINIMUM fire door assembly 3/4-HR = 45-minutes.
*A door closer and panic hardware may be required depending on the electrical panel amperage.
If it's determined a corridor, see footnote "b", for testing information
Kinda looks the same as Canada?
Need to know what type of occupancy and where the room is actually located
And is this existing, new, proposed
2015 IBC opening protectives - FIre barriers for a shaft with 1 hour fire resistant rating , 60 min opening protection required . If equipment room for elevator has to be rated the same as the shaft less than 4 stories (i.e. one hour fire barrier), then opening protectives would have to follow suite for a one hour fire barrier shaft.
(IBC section 713.4 - FIre resistance rating for shafts, 3005.4 for elevator machine room requirements, T. 716.5 Opening FIre Protection Assemblies - FIre Barrier having a required fire rating of 1 hour: Shafts min. rating for door = 1 hour)