Does anyone know of 1hr UL assmeblies for steel beams that are in a 1hr rated wood f-c assembly (L546 to be specific)? All SFRM, intumescent coating and even gyp surronds assemblies seem to have metal deck and concrete floor which L546 doesn't have.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I'm going by 2012 IBC 704.3. Do you know of code section telling individual encasement is not required/needed?Does the beam need individual encasement? Or is being in the assembly enough?
I'm going by 2012 IBC 704.3. Do you know of code section telling individual encasement is not required/needed?
It is construction type V-A so per table 601, Primary structural frame need to be 1 hr rated and the beams are part of the primary structural frame on the project.What section first says your situation requires the steel beams have to have one hour??
Is the building sprinkled?
The footnote in the Table 601 provides an exception for VA buildings
d. An approved automatic sprinkler system in accordance with Section 903.3.1.1 shall be allowed to be substituted for 1-hour fire-resistance-rated construction, provided such system is not otherwise required by other provisions of the code or used for an allowable area increase in accordance with Section 506.3 or an allowable height increase in accordance with Section 504.2. The 1-hour substitution for the fire resistance of exterior walls shall not be permitted.
Other wise encasement on all four sides may be required per 704.3 and 704.4
704.3 infers that if the beam is supporting only two floors or less, or a floor and roof or less, or a wall tow stories high or less, then individual encasement is NOT required. It can be protected by the typical membrane assembly of the one-hour floor-ceiling assembly.
704.3 Protection of the primary structural frame other than columns.
Members of the primary structural frame other than columns that are required to have protection to achieve a fire-resistance rating and support more than two floors or one floor and roof, or support a load-bearing wall or a nonload-bearing wall more than two stories high, shall be provided individual encasement protection by protecting them on all sides for the full length, including connections to other structural members, with materials having the required fire-resistance rating.
Exception: Individual encasement protection on all sides shall be permitted on all exposed sides provided the extent of protection is in accordance with the required fire-resistance rating, as determined in Section 703.
I see that we have not actually answered your original question, but instead we are trying to find ways to avoid individual encasement. Does anyone have commentary on the exception in italics above? I don't understand what it means.
704.3 infers that if the beam is supporting only two floors or less, or a floor and roof or less, or a wall tow stories high or less, then individual encasement is NOT required. It can be protected by the typical membrane assembly of the one-hour floor-ceiling assembly.
704.3 Protection of the primary structural frame other than columns.
Members of the primary structural frame other than columns that are required to have protection to achieve a fire-resistance rating and support more than two floors or one floor and roof, or support a load-bearing wall or a nonload-bearing wall more than two stories high, shall be provided individual encasement protection by protecting them on all sides for the full length, including connections to other structural members, with materials having the required fire-resistance rating.
Exception: Individual encasement protection on all sides shall be permitted on all exposed sides provided the extent of protection is in accordance with the required fire-resistance rating, as determined in Section 703.
I see that we have not actually answered your original question, but instead we are trying to find ways to avoid individual encasement. Does anyone have commentary on the exception in italics above? I don't understand what it means.