2 hour fire walls terminating at roof deck

Joined
Feb 21, 2024
Messages
7
Location
San Antonio
Plans calling for 1 hour protection of roof deck, 4' out per 706.6. Does all the structure need to be protected 4' out ? ie; BEAMS AND BARJOISTS ? primaries column to column ? or just 4' out ???
Milam
 
Does all the structure need to be protected 4' out ?
The structure supporting the portion of the roof 4’ out must be protected for its entire length:
2018 IBC 706.6 Exception 2:
2. Two-hour fire-resistance-rated walls shall be permitted to terminate at the underside of the roof sheathing, deck or slab, provided that:
2.1 The lower roof assembly within 4 feet of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour. [emphasis added]
That includes beams and bar joists, as well as the vertical elements supporting the beams and bar joists (such as columns and load-bearing walls.)
 