Referring to the GA-600-2006 Fire resistance design manual, specifically the generic 2 hour wall assembly "WP9206" which requires 4 layers of 5/8" type X gyp, staggered joints, specific screw spacing....
On the 3rd layer, there is a requirement for 1 7/8" screws at 12" o/c which would get it just through the layers below. Then there is a requirement over the 3rd layer for 1.5" wide steel straps at all vertical joints and intermediate channels (below the base layer) with 2 5/8" screws at 12" o/c
Here is the question:
Since there is no mention of spacing or staggering of the screws for the board its self, with respect to the screws for the straps, is it necessary to install the 12" o/c ones holding the drywall, as it would be duplicated by the screws holding the straps....
I am leaning towards, yes, it should be done exaclty as described, but wondering if anyone has any insight as to why. the gyp manual offers no explanation.
Thoughts??
On the 3rd layer, there is a requirement for 1 7/8" screws at 12" o/c which would get it just through the layers below. Then there is a requirement over the 3rd layer for 1.5" wide steel straps at all vertical joints and intermediate channels (below the base layer) with 2 5/8" screws at 12" o/c
Here is the question:
Since there is no mention of spacing or staggering of the screws for the board its self, with respect to the screws for the straps, is it necessary to install the 12" o/c ones holding the drywall, as it would be duplicated by the screws holding the straps....
I am leaning towards, yes, it should be done exaclty as described, but wondering if anyone has any insight as to why. the gyp manual offers no explanation.
Thoughts??