2" pressurized sewer crosses over 8" water main

jar546

CBO
Joined
Oct 16, 2009
Messages
13,435
Location
Not where I really want to be
They opted to sleeve the 8" water main below. This is one of the only times I feel the code allows the sewer to be above the water supply. This exception does not state that the sewer has to be below the supply unlike the normal requirement and exception.

16350601.jpg
 
If you're referring to IPC 603.2 exception 3, I can't find the corrugated plastic storm drain they used as a sleeve listed in tables 605.3, 702.2, or 702.3.
 