2003 A117.1 - Section 309.4
globe trekker
Seeking ya`lls input once again! :)
How many of you check Section 309.4 of the ICC/ANSI A117.1
code? On things like appliances (Residential or Commercial grade),
the knobs & other operating mechanisms, do you check for
compliance at plan review (if there are actual plans submitted),
..at the inspection, ..both, ...neither, ..other?
Appliances such as: microwaves, exhaust hoods, dishwashers,
washers / dryers, other..
Also, are the appliances "required" to have an ADA compliance
sticker / rating on them somewhere?
Thanks!
EXCEPTIONS:
1. Appliance doors and door latching devices shall not be required to comply with Section 309.4.
Question
Does it make sense to require the operating controls to be in reach if you can't open the door to use the appliance? Where is the logic?
We check "installed" appliances at time of final inspection.
Not all appliances are installed, microwaves, washers, dryers and dishwashers seem to be last minute installations by the tenants.
Thanks mtlogcabin for your input! I'm also wondering where the logic is
in regard to exhaust hoods. Even if there are compliant operating
controls/mechanisms (i.e. - pushbuttom type), can someone confined
to a wheelchair even operate an exhaust hood? Is a different type
control setup required, ..say, at a lower level for the wheelchair
community? Does the "reach range factor" apply to range exhaust
hoods? :confused:
globe trekker said:
Thanks mtlogcabin for your input! I'm also wondering where the logic isin regard to exhaust hoods. Even if there are compliant operating
hoods? :confused:
2009 IBC Accessibility and Usability for Residential Facitilites Workbook Editon: "Sections 1002.9 and 1003.9, Exception 6 allows for redundant controls: for example, the switch on the range hood can be out of the reach ranges if a wall switch is installed within the reach ranges."
Most all plans have the generic cut and paste claims so inspections are always necessary even if they do read the plans.
Francis
What about interior & exterior electrical panels?
QUESTION # 1: Do the "reach range" requirements also apply
to heights of the circuit breakers? (RE: Article 404.8 in the 2008
NEC)
QUESTION # 2: Is an Accessible pathway required to the exterior
electrical panel ? (RE: Section 1104, or others in the 2006 IBC)
QUESTION # 3: As an employee of a business, should it be
required to provide me with an Accessible route to the electrical
panels (interior or exterior)?
Thanks for your input! :)
As a reminder the IBC tells you when and where and the ANSI tells you how to meet the standards.
Q 1 & 2:
A. 1002.9 "electrical switches" are general use IMO, not disconnects for servicing appliances and equipment.
Q 3: No, see 1103.2.9 Equipment spaces for service personnel not required to be accessible.
Francis
Doing a plan review of an accessible apartment structure now. Just a short time ago (this morning) added a comment requesting details of the kitchen appliances to demonstrate code compliance.