I have a team of architects and engineers that are of the understanding that believe that fire dampers are not required where a fully 26GA ducted system crosses a 1 hr fire barrier but has openings on both sides.....We have always interpreted (and been taught)this section to mean the ductwork is continuous through side "A" and only has openings on side "B", not both sides....Upon further reading, I can see how this can be interpreted both ways....Any input?
717.5.2 in 2012 codes
716.5.2 Fire barriers.
Duct and air transfer openings of fire barriers shall be protected with approved fire dampers installed in accordance with their listing.
Exception: Fire dampers are not required at penetrations of fire barriers where any of the following apply:
1. Penetrations are tested in accordance with ASTM E 119 as part of the fire-resistance-rated assembly.
2. Ducts are used as part of an approved smoke control system in accordance with Section 909.
3. Such walls are penetrated by ducted HVAC systems, have a required fire-resistance rating of 1 hour or less, are in areas of other than Group H and are in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2. For the purposes of this exception, a ducted HVAC system shall be a duct system for conveying supply, return or exhaust air as part of the structure’s HVAC system. Such a duct system shall be constructed of sheet steel not less than 26 gage thickness and shall be continuous from the air-handling appliance or equipment to the air outlet and inlet terminals.
717.5.2 in 2012 codes
716.5.2 Fire barriers.
Duct and air transfer openings of fire barriers shall be protected with approved fire dampers installed in accordance with their listing.
Exception: Fire dampers are not required at penetrations of fire barriers where any of the following apply:
1. Penetrations are tested in accordance with ASTM E 119 as part of the fire-resistance-rated assembly.
2. Ducts are used as part of an approved smoke control system in accordance with Section 909.
3. Such walls are penetrated by ducted HVAC systems, have a required fire-resistance rating of 1 hour or less, are in areas of other than Group H and are in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2. For the purposes of this exception, a ducted HVAC system shall be a duct system for conveying supply, return or exhaust air as part of the structure’s HVAC system. Such a duct system shall be constructed of sheet steel not less than 26 gage thickness and shall be continuous from the air-handling appliance or equipment to the air outlet and inlet terminals.