My questions are with how do they operate in compliance "if/when" they are not bolted together. If the top leaf is already open, does it automatically open against the wall to the point it is no longer a protruding object from the pull-approach side? If the top leaf is only open 45 degrees and bottom leaf is closed at 0 degrees, or fully open at 90 degress, how does this meet accessibility (protruding objects) and operations (special knowledge or effort) compliance When only the top leaf is open, the door is no longer 80 inches in height?
1008.1.1. Size of doors. ...The height of doors shall not be less than 80 inches.
It gets tricky when the door is rated (I know this one isn't, but for future reference), because some door manufacturers test their rated dutch door with both the top and bottom leaf latching into the jamb. This application requires 2 motions to unlatch, and the motions have to be simultaneous. There is at least one manufacturer who has tested with the top leaf latching into the bottom on a rated door, and this meets egress requirements as well as passing the fire test.