• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2009 beauty salon and pet shop ventilation

klarenbeek

Silver Member
Joined
Jan 28, 2010
Messages
422
Location
Sioux Falls, SD
Has anyone caught the footnote changes for pet shop and beauty salon ventilation in table 403.3 of 2009 IMC? Footnote b requiring no recirculation of air now includes pet shops and ALL beauty salons, not just nail salons. Just had the first one come thru under the new requirements. Fortunately it was a small salon pulling off a larger system, so they can get away with just exhausting out the air supplied to the space. For a larger salon or a pet shop with an independent system, this is a huge change. Thoughts?
 
That is it the code has gone to the dogs

I guess it makes it clearer on nail places instead of trying to design gor the nails only you design for the entire space
 
Highly effective nail dust, vapor/odor and airborne pathogen source capture system. With 200 cfm of suction at the capture hood, Healthy Air™ Nails Source Capture System provides 4 times the required airflow. Nail Salon Ventilation Regulation Changes:

2012 International Mechanical Building Code (IMC) Table 403.3 (h)

(h) For nail salons, each nail station shall be provided with a source capture system capable of exhausting not less than 50 cfm per station.

http://aerovexsystems.com/air-ventilation-resources/outside-ventilation_salon-codes.asp

Source Capture Change Significance:

Footnote "h" to Table 403.3 has been modified to require nail salons to have a source capture system at each nail station. Based on the definition of "Source Capture System", the exhaust from a station in a nail salon is required to capture the air contaminants at their source and terminate them to the outdoor air.
 
Please keep in mind that this does not mean spaces applicable to footnote b must be provided with 100% outdoor air systems. Footnote b states that "recirculation of air FROM such spaces is prohibited." Meaning that you cannot take air from this space and recirculate it into the space next door. You are permitted to recirculate this air within the space. The outdoor air and exhaust air associated with beauty salon, nail salon, or pet shop is calculated to remove the contaminants. If you have an independent system that provides 25% outdoor air, the remaining 75% can be recirculated within the space, but cannot be recirculated from the space to another space. I like to use the example of a bakery kitchen. You want to have the aromas of the bakery to drift out into the customer area of the bakery, but you do not want to have those aromas recirculated into the weight loss center next store :)
 
Has anyone caught the footnote changes for pet shop and beauty salon ventilation in table 403.3 of 2009 IMC? Footnote b requiring no recirculation of air now includes pet shops and ALL beauty salons, not just nail salons. Just had the first one come thru under the new requirements. Fortunately it was a small salon pulling off a larger system, so they can get away with just exhausting out the air supplied to the space. For a larger salon or a pet shop with an independent system, this is a huge change. Thoughts?
 
Do you know if you can use PVC to exhaust the fumes through the walls to the exhaust fan
 
So my partner has a hair salon we put PVC duct Underground through the wall up to the exhaust fan The Village came in and said you cannot use PVC in the walls is there any code that supports that I can use PVC
 
Top