joetheinspector said:
On a new commercial project there are guard rails that have the posts 4ft apart with aircraft wire strung horizontally. The wire has an opening that is 3 and ¾ of an inch at the post. In the middle of the posts the opening is less than 4inches, however, the wire can be stretched to allow a 4inch sphere to pass through. My question is do you know how to test this to see if it complies with code or not? Are there other code sections in regard to this other then the one below1607.7.1.2 Components.
Intermediate rails (all those except the handrail), balusters and panel fillers shall be designed to withstand a horizontally applied normal load of 50 pounds (0.22 kN) on an area equal to 1 square foot (0.093 m2), including openings and space between rails. Reactions due to this loading are not required to be superimposed with those of Section 1607.7.1 or 1607.7.1.1.
Sorry for being late to the party;
Joe, I will first say if you have read the other 2 previous threads you will have a good idea were the myth and truth start and stop.
However I will add the following brief notations, as if I could ever be brief with additional notes:
- First off ask for information on the cable fasteners and or system manufactures specifications fittings. In other words the cable fitting manufacture, if they are any good they publish base specifications. Feeney & Ultra-Tec both publish guidelines for distance between cables, distance between verticals supports & tension on the cables. Others do also, but they are the 2 main manufactures in the USA.
- If they purchased and installed a complete product, meaning a mass produced guard frame with cable infill, Feeney Architetural is one manufacture, then that cut sheet should be good IMO as it will give you all that information also.
- Then look to see if they have a tensioning plan, I always tell inspectors, ask the installers in a curious way, Hum whats the process you used for tensioning the cables. If they can spell it out and don't look dumb founded by the question, its a good sign. My main installer has it down in his sleep all by feel. I had a town we did 3 installations, the inspector wanted us to show tension with a gauge, over 70 spot checks at 3 different locations we didn't miss a one, needless to say he got off our back.
So with that said, before you go in to having a test done, have them produce the fitting manufactures documentation for centerline spacing between holes, max distance between verticals and also max distance on a single run, length of cable. If the produce falls in to those specifications, then question them on how they tensioned the cables, per fitting manufactures specs.
If all that falls in to place and they produced sealed drawings and the installation matches the drawings, I am not sure more is needed.
Now with that said, Pretty much every commercial cable installation our firm has done is based on using 3/16" diameter cable, set at a maximum of 3-3/8" on center with a maximum of 46" between vertical stablizers. We also tension are cables for commercial to about 400lbs, why because when we do the ASTM E935 cone test for spreading of infill (Not in the code), these specifications passed during physical testing. Both Feeney & Ultra-Tec have specifcations based on meeting 125lbs pulling on a 1sqft panel and then checking for 4" sphere. So those specs also work well to their published tensions and spacing. Ultra-Tec also publishes an engineers paper which uses the 50lbs on a 1 sqft area and figures the percentage of a 4" flat circle and comes up with about 12.75 lbs of force, however I am not a big fan of this because 4" flat circle is not the same as the edge of a sphere.
However, check those specs by the fitting manufactures, because 1/8" diameter cable and 3/16" diameter cable both have different parameters and most publish the 1/8" spec for all cables, and yes the stronger cables can go a little bigger.
Also note when reading the specifications which braid of cable they are installing. A 1x19 braid is much stiffer than 7x7 braid and hence you need to look at that also.
Also if they can't produce a fitting manufactures spec, I would ask for how they came up with the spacing and tension they are doing and who engineered it?
Here are a few links for additional
http://www.artisticrail.com/CableRailings.htm Here are a few examples we did, if you then navigate to the glass railings and scroll down to picture GR-12 you will see a job we did at a Staples were my men are running cables on the stairs.
http://thecableconnection.com/metal-framed-railings.html Here is Ultra-tecs page on their installation parameters
http://www.feeneyinc.com/Technical-Documents#CableRail Here is the link to Feeney's documentation.
Now with all that said, you are able with the proper framework and tension to go a little larger and wider, but if not per manufacture spec, then get an engineers complete drawing set, not only base design but every piece listed on drawings and have them list tension on cables also.
I hope this helps - but in short, there is no force applied to the sphere in the IBC, the sphere is only for size without force.
Tom