OK, Stepped Buildings, Exception 1.........says you can terminate a fire wall at the underside of of the roof sheathing, if;
The lower roof assembly within 10 feet (3048 mm) of the wall has not less than a
1-hour fire-resistance rating and the entire length and span of
supporting elements for the rated roof assembly has a fire-resistance rating of
not less than 1 hour.
So, I read this that, the rafter or truss carrying the 1-hr assemble needs to be supported to equally protected bearing walls, regardless is it exceeds the minimum 10'. I have a designer saying that, no, he only needs to protect the required 10' of roof rafters/trusses, after that it can be unprotected. I think the code is pretty clear.............. What say ye?
The lower roof assembly within 10 feet (3048 mm) of the wall has not less than a
1-hour fire-resistance rating and the entire length and span of
supporting elements for the rated roof assembly has a fire-resistance rating of
not less than 1 hour.
So, I read this that, the rafter or truss carrying the 1-hr assemble needs to be supported to equally protected bearing walls, regardless is it exceeds the minimum 10'. I have a designer saying that, no, he only needs to protect the required 10' of roof rafters/trusses, after that it can be unprotected. I think the code is pretty clear.............. What say ye?