507.1 General.
The area of buildings of the occupancies and configurations specified in Sections 507.1 through 507.12 shall not be limited.
Exception: Other occupancies shall be permitted in unlimited area buildings in accordance with the provisions of Section 508.2.
507.3 Sprinklered, one story.
The area of a Group B, F, M or S building no more than one story above grade plane of any construction type, ..., shall not be limited ... How are you interpreting section 507.3 for unlimited area buildings. Based on the sentance structure it would appear that you could have a group B or a group F or a group M or a group S since other sections in 507 use "and" when more than one occupancy is allowed in an unlimited area building. But there are sections in 507 that use "and" when "or" might be a better choice. The whole section 507 is inconsistent in how and/or when more than one occupancy is allowed without tripping the 507.1 Exception for "other occupancies".
I have a designer that is saying any or all of the four listed occupancies can be unlimited area in this building without tripping the 507.1 exception.
You thoughts and code sections are appreciated.
The area of buildings of the occupancies and configurations specified in Sections 507.1 through 507.12 shall not be limited.
Exception: Other occupancies shall be permitted in unlimited area buildings in accordance with the provisions of Section 508.2.
507.3 Sprinklered, one story.
The area of a Group B, F, M or S building no more than one story above grade plane of any construction type, ..., shall not be limited ... How are you interpreting section 507.3 for unlimited area buildings. Based on the sentance structure it would appear that you could have a group B or a group F or a group M or a group S since other sections in 507 use "and" when more than one occupancy is allowed in an unlimited area building. But there are sections in 507 that use "and" when "or" might be a better choice. The whole section 507 is inconsistent in how and/or when more than one occupancy is allowed without tripping the 507.1 Exception for "other occupancies".
I have a designer that is saying any or all of the four listed occupancies can be unlimited area in this building without tripping the 507.1 exception.
You thoughts and code sections are appreciated.