klarenbeek
REGISTERED
Doing a plan review for a project that will be under the 2012 IMC. In the 2012 code, exception 3 under fire barriers (607.5.2) allowing for no fire dampers if the duct system contains no flex has been extended to the fire partion section (607.5.3) as well, as exception 4. The new exeption is identical word for word to the existing exception for fire barriers.
Here's the situation--1 hour rated corridor where the walls are fire partions partitions. If there is no flex in the system, a smoke damper only, no fire, is required at the wall penetration because of the new exception. This corridor also has duct registers in the floor, coming from the lower level.
Question- Do the floor penetrations require smoke dampers only or fire/smokes? Does the exception apply to the walls only or the floor/ceiling assembly as well?
Here's the situation--1 hour rated corridor where the walls are fire partions partitions. If there is no flex in the system, a smoke damper only, no fire, is required at the wall penetration because of the new exception. This corridor also has duct registers in the floor, coming from the lower level.
Question- Do the floor penetrations require smoke dampers only or fire/smokes? Does the exception apply to the walls only or the floor/ceiling assembly as well?