The change to "story" from "floor area" has major consequences or have I been interpreting incorrectly that the floor area is limited to the fire area?
2012
[F] 903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the floor area where the Group A-1, A-2, A-3 or A-4 occupancy is located, and in all floors from the Group A occupancy to, and including, the nearest level of exit discharge serving the Group A occupancy.
2015
[F] 903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories from the Group A occupancy to, and including, the levels of exit discharge serving the Group A occupancy.
Gregory R. Keith, Professional heuristic Development, representing The Boeing Company, requests Approval as Modified by this Public Comment.
Further modify the proposal as follows:
903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story (delete floor) where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories (delete floors) of the building from the Group A occupancy to, and including, the nearest level of exit discharge serving the Group A occupancy. For Group A-5 occupancies, the automatic sprinkler system shall be provided in the spaces indicated in Section 903.2.1.5.
Commenter’s Reason: This public comment for approval as further modified is intended to be entirely editorial in nature. It replaces the term “floor(s)” with the term “story(s)” in two locations. Floor is not a defined term in the IBC or IFC. Story is a defined term: “That portion of a building included between the upper surface of a floor and the upper surface of the floor… Additionally, Section 903.2.1 refers to the “level of exit discharge.” That term is defined as, “The story at the point at which an exit terminates and an exit discharge begins.” Replacement of the term “floor” with the term “story” will be consistent with current IBC/IFC terminology and will assist code users by clarifying the application of this important provision.
https://www.iccsafe.org/wp-content/uploads/06-IFC1.pdf
The change to "story" from "floor area" has major consequences or have I been interpreting incorrectly that the floor area is limited to the fire area?
2012
[F] 903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the floor area where the Group A-1, A-2, A-3 or A-4 occupancy is located, and in all floors from the Group A occupancy to, and including, the nearest level of exit discharge serving the Group A occupancy.
2015
[F] 903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories from the Group A occupancy to, and including, the levels of exit discharge serving the Group A occupancy.
Gregory R. Keith, Professional heuristic Development, representing The Boeing Company, requests Approval as Modified by this Public Comment.
Further modify the proposal as follows:
903.2.1 Group A. An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story (delete floor) where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories (delete floors) of the building from the Group A occupancy to, and including, the nearest level of exit discharge serving the Group A occupancy. For Group A-5 occupancies, the automatic sprinkler system shall be provided in the spaces indicated in Section 903.2.1.5.
Commenter’s Reason: This public comment for approval as further modified is intended to be entirely editorial in nature. It replaces the term “floor(s)” with the term “story(s)” in two locations. Floor is not a defined term in the IBC or IFC. Story is a defined term: “That portion of a building included between the upper surface of a floor and the upper surface of the floor… Additionally, Section 903.2.1 refers to the “level of exit discharge.” That term is defined as, “The story at the point at which an exit terminates and an exit discharge begins.” Replacement of the term “floor” with the term “story” will be consistent with current IBC/IFC terminology and will assist code users by clarifying the application of this important provision.
https://www.iccsafe.org/wp-content/uploads/06-IFC1.pdf