2016 CBC vs. 2016 CPC
Kris Johnson
Sacramento, CA
I am working on a spreadsheet that calculates occupant load and plumbing fixture counts based on room types and their square footages (see link to picture below). The problem I am running into is how to translate a "Function of Space" from CBC Table 1004.1.2 into a Plumbing "Occupancy" from CPC Table A. Below is a second link to a picture comparing the two and as you can see it has several holes. Anyone know where I can find the information to fill out the rest?
For example: In the building code a skating rink is an A-4, but there is no A-4 on Table A in the plumbing code.
https://www.dropbox.com/s/qdograta0mivfb9/Building Analysis 01.JPG?dl=0
https://www.dropbox.com/s/efr6kris49u6y83/Building Analysis 02.JPG?dl=0
Thank you,
Kris
Welcome
Not a plumber, but sometimes there are so many scenarios with codes, it is hard to develop cheat sheets
Thanks for your contribution
The function of space does not directly correlate with occupancy group. For example, you show that an unconcentrated assembly without fixed seats is automatically a Group A-2, but an unconcentrated assembly without fixed seats can be a lobby (Group A-3 if over 49 occupants) or a conference room (Group B if less than 50 occupants).
Your example shows four exercise rooms. Two of those have occupant loads greater than 49, and are correctly classified as Group A-3. The other two have occupant loads less than 50, and these would not be classified as Group A, but as Group B per Section 303.1.2, subparagraph 1 (2015 IBC).
Another thing I noticed is that the square footage column is marked as "Net." Most occupant load factors do not apply to net floor areas, but to gross floor areas.