Section 705.2
Cornices, eave overhangs, exterior balconies and similar projections extending beyond the exterior wall shall conform to the requirements of this section and Section 1405 respectively.
There is no explicit definition for an exterior balcony in the code. How does Section 705.2 apply to typical balconies in multifamily construction where they may be partially or fully recessed? What is the definition of an exterior wall in this context?
Section 705.2.3.1 Exception #3
Balconies and similar projections on buildings of Types III, IV, and V construction shall be permitted to be of Type V construction and shall not be required to have a fire-resistance rating where sprinkler protection is extended to these areas.
I am trying to determine if ALL exterior balconies in Type III, IV, and V construction can be non-rated under Exception 3.