We are working on a courtyard style multi-family project. Our plan reviewer is requesting we provide an STC 50 wall at the exterior of the building where it is adjacent to an exterior corridor/egress balcony. I spoke with an acoustical consultant who basically said the wall rating would be negligible due to the openings door/windows and this is not a viable request. I reread IBC 1206 which notes that it covers room-to-room sound transmission. The scoping section also notes the section shall apply to interior walls, partitions and floor ceiling assemblies...
I do not think this section is intended to be applied to exterior wall conditions and there are no STC requirements in the exterior wall section of the IBC. I am preparing to make my case to the reviewer and was wondering if anyone else has come across this issue.
This is 2018 IBC, R-2 Occupancy.